2 breakers wired to a single circuit

david5687May 17, 2010

I'm doing some renovation work and have encountered a strange situation (to me) while mapping out the main breaker panel.

On more than a few outlets and lights, two circuit breakers must be on for the outlet or light to be "on". This is not for all circuits, but for well more than 1/2 of the house at 120V, including my swimming pool pump (240V). There are two circuit breakers marked "main lights" in particular in which one of them has to be on in conjunction with another one on the panel which seem to be the main culprits.

My question is, how concerned should I be with this wiring? Is it normal/acceptable? The house was constructed in 1927 and is a mixture of K&T and Romex. The dual breaker situation seems to exist in both types of wiring.

Thank you for reporting this comment. Undo
bus_driver

While your panel could really be wired incorrectly, it also is possible that it is a "split bus" in that most/all of the 240 volt circuits have no main disconnect but the 120 volt circuits do have a main disconnect ahead of the individual circuit overcurrent protection. The result is that disconnecting all loads in the panel might require operating up to 6 circuit breakers. The NEC in 1984 changed so that split bus is no longer used for new installations but existing split bus installations are not required to be changed so long as they are in good condition.

    Bookmark   May 18, 2010 at 7:32AM
Thank you for reporting this comment. Undo
Ron Natalie

As BUS points out "MAIN LIGHTING" is a common label for the feed to the "bottom" half of these split bus panels. (The assumption is that the other stuff on the "top" half are things like stoves, dryers, and other larger loads).

    Bookmark   May 18, 2010 at 7:59AM
Thank you for reporting this comment. Undo
hendricus

On first reading I took this to be multi-wire branch circuits where two hots go out and one neutral returns. If the two breaker handles are tied together both would be switched on or off. This would account for the mention of the swimming pool pump.

Just my take.

    Bookmark   May 18, 2010 at 8:41AM
Sign Up to comment
More Discussions
Badly done multi-wire circuits (previous owner strikes again..)
I bought a 1940-ish house last year, for which the...
quahog
Disposer Power Cord
I recently bought a GE disposal online. The model is...
africanboy
can homeowner so electrical work in his own home ? (above ground pool)
I live in Western ma and I'm having an Adobe ground...
growingadvice
Can you make a splice inside one of these?
The reason I ask is my neighbor's house was destroyed...
schreibdave
Power to shed
Looking to run one 20 amp circuit to my shed and I'm...
ohio45424
Sponsored Products
WA 3528 Quad Row LED Strip Light 450/m 28mm wide Foot
EnvironmentalLights.com
My New Flame Rechargeable LED Candle by Ingo Maurer
$600.00 | Lumens
Thermostatic Shower System, 12 Ceiling Apron, Handshower & Jet Sprays
Hudson Reed
Tech Lighting | Cheers Pendant
$124.00 | YLighting
54" Fanimation Zonix Satin Nickel Ceiling Fan
Lamps Plus
Designers Fountain 5695 Palladium 5 Light Chandelier in Pewter Finish - 5695-PW
$261.90 | Hayneedle
© 2015 Houzz Inc. Houzz® The new way to design your home™