40 amp manual A-B switch

penoirMay 25, 2010

I currently have 2 200 amp service panels; Panel A runs all lighting, outlets and equipment in the house. Panel B is an interruptible service and runs the geothermal heating & cooling, and hot water. What I would like to do is this: I want to connect the stove top & oven to the interruptible panel (panel B) I'm looking for a manual way to be able to leave the oven and cook top connected to panel A, but also have access to powering it through panel B. There is room physical for additional breakers in the Panel B, but amp wise it is maxed out (that is why I want an A/B switch). I need a switch that will handle 40 amps. IÂm looking for a manufacturer &/or part number that I can order.

Thank you for reporting this comment. Undo
Ron Natalie

Lets hold on a second here. What do you mean "ampwise" it's maxed out. Have you done a real load calculation or are you just summing up the breakers in that panel?

Even if you were "maxed out" what good would this "switch" do?

Large double throw switches are availble, but the price will probably be scary to you. The cutoff is about 30A for the kind that mounts in a regular box versus the ones that come in their own NEMA enclosure (and the accompanying price jump).

If you're really determined, your cheapest answer would be a 40A DPDT Intermatic timer (whether you chose to use the "timer" part of it or not).

    Bookmark   May 26, 2010 at 6:30AM
Thank you for reporting this comment. Undo
cuffs054

Why would you want to do this?

    Bookmark   May 26, 2010 at 7:11AM
Thank you for reporting this comment. Undo
brickeyee

"There is room physical for additional breakers in the Panel B, but amp wise it is maxed out"

Based on what?

The sum of the breaker ratings in the panel?

Only an actual load calculation can determine if the panel is "maxed out," not adding up ratings of breakers.

    Bookmark   May 26, 2010 at 7:20AM
Thank you for reporting this comment. Undo
penoir

the max load calculation is 180 amps in panel B, however after I have turned off one of the hot water heaters (only my wife & I) and because we have both a geothermal boiler for in floor radiant heat and a forced air geothermal unit I disconnect one of the units using the manual breaker mounted on the wall next to the geothermal units. The main reason I want to do this is cost conservation. interuptable power is much less expensive, but on the rare occasion we have a full house I'd want be able to put the stove top and oven back onto panel A.

    Bookmark   May 26, 2010 at 8:09AM
Thank you for reporting this comment. Undo
joed

A transfer switch like used for generator installtions sould do the job for you.

    Bookmark   May 26, 2010 at 8:15AM
Sign Up to comment
More Discussions
Want to save shower recessed light
I have 2 matching recessed lights in my bathroom. One...
africanboy
Need to Understand GFCI Requirements.
I posted this in the remodeling section, but I think...
homechef59
Dryer power cord next to vent
My contractor is enlarging the dryer vent hole in the...
phil2015
Light/Switch wiring
Here is the scenario. Have a kitchen light that needs...
wgl3333
Inspection Report
Had a gorgeous 1909 house inspected yesterday and don't...
cmae17
Sponsored Products
Lattice Swivel Armless Bar Stool, Black
Zuri Furniture
LBL Boardwalk 18" High Black Outdoor Wall Light
Euro Style Lighting
Le Klint | Le Klint Pendant 175A
$555.00 | YLighting
Metal Sun Tray Set
$49.99 | zulily
Wire mesh four horizontal cubbies w/wooden top
Origin Crafts
Patio Living Concepts Outdoor Lighting. Seaside Outdoor 34 in. White Table Lamp
Home Depot
Indoor Ceiling Fans: Hunter Stratford 44 in. Brushed Nickel Ceiling Fan 28688
$99.97 | Home Depot
Kichler Sunset II 40" Round Wall Mirror
Lamps Plus
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™