Have an old house with knob and tube wiring that has had newer wiring added over the years, hard telling what's behind those walls. Have some gfci's that show reverse polarity. The wiring seems correct(black is showing it is hot and on the correct side of gfci). Switched wires, same results. Even put new gfci in. I am stumped. Anyone ever had a similar situation. House is to be inspected and needs to have this fixed.

Thank you for reporting this comment. Undo
brickeyee

A missing ground conductor will cause incorrect readings on many 'receptacle testers.'

    Bookmark   May 6, 2010 at 6:30PM
Thank you for reporting this comment. Undo
Ron Natalie

Without a ground there's no way to tell polarity. You have to have a reference.
As brickeye points out, having unterminated connections will cause enough induced voltage to trigger a high impedance meter or light up the little bulbs in these things.

To be sure, find some known ground (perhaps a water pipe) and measure between the small slot and that (should be 120V) as well as between the two slots.

    Bookmark   May 7, 2010 at 8:00AM
Sign Up to comment
More Discussions
ARGH! no boxes
Went over to my daughter's house to help them change...
Ron Natalie
electrical outlet distance to radiator
how far from a radiator should a wall electrical outlet...
amsayan
new wiring project
I have a water damaged room I will soon be renovating....
CharlesInVT
A/C wired to main panel only?
I had 2 electricians come out to bid upgrading my service...
frank_diy
Crawl Space Junction Boxes: inspection and capping
Hello. I'm in the process of crawl space improvement....
SparklingWater
© 2015 Houzz Inc. Houzz® The new way to design your home™