Connecting Subpanel to Main Panel

tom418May 10, 2012

I'm adding a subpanel onto my GE TM2020CCU. The subpanel most likely will be a GE TLM1212CCU, for the purpose of feeding four electric baseboards (1500w and three 750 watts), and a water heater.

A GE THQL 2160 60-amp double pole breaker in the main panel

will protect the sub.

My questions:

I plan on using a 4 inch long x 1.25 inch offset nipple between the two boxes. I'll be using #4 THHN to connect the two boxes. Should my ground be #4 BARE or Green? (Can it be #6?

Is this a better way to provide ground to the subpanel (as opposed to grounding through the nipple)?

Note: I plan on using grounding bushings on both ends of the offset nipple, to be connected to the ground bars of each box. Yes, I know that the ground and neutral must be isolated from each other in the subpanel :)

Thank you for reporting this comment. Undo
Ron Natalie

Either bare or green is fine. Given the short run, I'd just run a grounding conductor between the two respective ground terminals. You only need a #10 ground here. You only need #6 for the feeder conductors as well.

    Bookmark   May 11, 2012 at 11:25AM
Thank you for reporting this comment. Undo
tom418

Thanks!

    Bookmark   May 11, 2012 at 3:48PM
Sign Up to comment
More Discussions
Please Critique Low-Volt (Home Automation) Plan/Proposal
GW/Houzz Community, As always, I want to thank this...
Andrew K.
Spa Capacitor question
My spa is wired for 220v. The pump motor is rated for...
pugmark
Does a refrigerator need to be on a separate circuit?
Does a refrigerator need to be on a separate circuit?...
rontero
A/C wired to main panel only?
I had 2 electricians come out to bid upgrading my service...
frank_diy
Motion sensor that doesn't click
I have a motion sensor very much like the picture attached...
drmeow3
© 2015 Houzz Inc. Houzz® The new way to design your home™