Cable Size for Subpanel

normanbestMay 30, 2012

I am adding a 4 circuit subpanel right next to my main panel. The subpanel will have 2 20amp circuits and 2 15amp circuits. What size cable do I have to run from the main to the sub?

Thanks

Thank you for reporting this comment. Undo
hendricus

Depends on what you are feeding with the 20 and 15 amp circuits.

Myself, I would put in a 40 amp breaker with a #8 4 wire cable. It's called 3 wire with ground.
That's 2 hot 1 neutral and 1 ground.