Outdoor connections

jscozzMay 14, 2013

Is there any compound that should be used on outdoor connections to prevent any oxidation or moisture from getting in to them? Mainly connections inside 3R enclosures to lugs or breakers.

I know there is NoOx for Al to Cu connections... but I have read that NoOx should not be used on non-Al connections. Something like the gel that is in the exterior blue wire nuts for outdoor use.

Or is it better to just use nothing at all on outdoor copper to panel lug/breaker connections?

Thank you for reporting this comment. Undo
brickeyee

A correctly installed wire nut is a gas tight connection.

I try to leave them pointing up to limit water collecting in them.

Nothing is actually required.

    Bookmark   May 15, 2013 at 6:16PM
Thank you for reporting this comment. Undo
elltwo

I think the OP is asking about terminations on a breaker or bar, not wire to wire splices.

    Bookmark   May 16, 2013 at 9:48AM
Thank you for reporting this comment. Undo
brickeyee

When torqued correctly the typical set screw connection in a panel is also gas tight.

You do have a torque wrench or torque screwdriver for torquing connections I hope.

The aluminum wire debacle of the 1970s called called attention to the general failure to enforce torque limits on connections.

The need to use low temper aluminum on single wire connections (as opposed to stranded) heightened the problem.
The aluminum heats up, expands, and deforms enough to reduce the connection integrity. It shows up as screws that are no longer 'tight.'

The next cycle makes it worse since the connection is no longer gas tight and becomes mechanically inadequate.

Harder aluminum would have resulted in solid conductor cables that did not have adequate flexibility for their intended use.

    Bookmark   May 16, 2013 at 11:12AM
Thank you for reporting this comment. Undo
mike_kaiser_gw

I'm curious how many of the professionals here have a torque screwdriver and how often they use it.

    Bookmark   May 16, 2013 at 11:23PM
Thank you for reporting this comment. Undo
brickeyee

I have a couple of AHJs that come through torque wrench in hand and spot checks, especially breakers and neutral and ground bars, but occasionally a receptacle.

The screwdrivers are enough of a PITA and overpriced that using a wrench is a good option.

As long as you only use straight extensions it still gives correct readings, and for larger values (like 4/0 clamps) is easier to use.

    Bookmark   May 17, 2013 at 9:20AM
Sign Up to comment
More Discussions
Can you make a splice inside one of these?
The reason I ask is my neighbor's house was destroyed...
schreibdave
Wireless light switch for switched outlet?
So we have no overhead lighting in any of our bedrooms,...
vikingshelmut
Please Critique Low-Volt (Home Automation) Plan/Proposal
GW/Houzz Community, As always, I want to thank this...
Andrew K.
Goodbye Phone Jack: what to do with wires?
We want to remove this phone jack. It's in a useless...
maggiepatty
Humming Transformer
Last summer the POCO replaced the transformer on the...
mike_kaiser_gw
Sponsored Products
Kichler Lighting 11019PR Cameron Prarie Rock Outdoor Wall Sconce
Littman Bros Lighting
6' Red Cedar Royal Highback Porch Swing with Stand
Fifthroom.com
Goldtone Heart Ornament
$16.99 | zulily
Tessa Tiered Serving Stand in Antique Brass
| Dot & Bo
Stone Stool
Lightology
Orbit Area Rug
Home Decorators Collection
Round Side Mount Replacement Canopy
$279.00 | FRONTGATE
Armstrong Three-Light Rubbed Bronze Outdoor Large Downward Wall Lantern with Cle
$308.00 | Bellacor
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™