electric baseboard wiring

procaelioMay 15, 2011

I have a 2 pole 20amp breaker. I want to supply power to two baseboard heaters (1800 watt total) in two different rooms with separate programable wall thermostats. Can I run a 12/2 wire to a junction box and two wires from the junction box, one to each of the two thermostats.

Thank you for reporting this comment. Undo
kurto

If these are truly 900 watts each, running on 240 volts, then yes, you can run a 12/2 cable to a junction box and feed both thermostats.

    Bookmark   May 15, 2011 at 6:19PM
Thank you for reporting this comment. Undo
bus_driver

For heater loads, the maximum wattage for a 20 amp circuit at 240 volts is 3840.

    Bookmark   May 15, 2011 at 8:02PM
Thank you for reporting this comment. Undo
procaelio

Yes, the wattage is well below maximum. I just need to know if it was ok to split the line before the thermostats. Thanks

    Bookmark   May 16, 2011 at 12:07AM
Thank you for reporting this comment. Undo
Ron Natalie

Yep, you can split the line in any place that's legal to make such a junction. This will be an accessible box (perhaps one at the heater, perhaps at the thermostat, or perhaps somewhere else). In some cases you might be able to do so inside the enclosure of one of the heaters.

    Bookmark   May 16, 2011 at 9:25AM
Sign Up to comment
More Discussions
Re-wiring range to service spa
what connectors are appropriate for joining 6-3 NMB...
justsomeotherdude
Looking for Ideas For Lighting at base of 300' long driveway
Sorry for the "picture through the screen"...
dixieman
Too much load for circuit?
I have 200 amp service to the main panel (which has...
zver11
Does a refrigerator need to be on a separate circuit?
Does a refrigerator need to be on a separate circuit?...
rontero
electrical outlet distance to radiator
how far from a radiator should a wall electrical outlet...
amsayan
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™