240 volt vs 120 volt

woodturner79May 7, 2012

I got a new bandsaw. The motor can be wired to run at either 120v or 240v. My friend told me I should wire it 240 because the motor will start and run better.

I realize at 240v it will pull less amps, but will it really be beneficial in any other way? Will it really run better at a higher voltage?

Thank you for reporting this comment. Undo
brickeyee

How large is the motor(horsepower on the motor nameplate) and what type motor?

Full size bandsaws typically use an induction motor int eh1 to 1.5 horsepower range.

Operation would be exactly the same IF the voltage does not change under start-up and running.

Motor start-up is the usually the issue.
The motor pulls far more current briefly as it tries to come up to speed,and this results in more voltage drop in the wires feeding the motor, the centrifugal switch contacts, and increased heating of the start winding.

On 240 V the motor will come up to speed faster with about half the current needed at 120 V.

    Bookmark   May 7, 2012 at 9:42AM
Thank you for reporting this comment. Undo
randy427

It would only be a factor with heavy use. If my shop didn't already have a 240 outlet, I wouldn't rewire my shop to provide one.

    Bookmark   May 7, 2012 at 9:45AM
Thank you for reporting this comment. Undo
woodturner79

It's a 1 HP motor. I'm not sure what you mean by type but it has a large capacitor on the motor that I was told helps it on starting?
wiring it for 240 is not an issue at all. It only involves changing some wires in the junction box on the motor. I have to run a new circuit for it anyway and have no problem putting it at 240. I just wondered if it would be beneficial at all and really help it to run better.

    Bookmark   May 7, 2012 at 11:15AM
Thank you for reporting this comment. Undo
brickeyee

"a large capacitor on the motor that I was told helps it on starting? "

Sounds like a standard 1-phase induction motor.

If you look on the nameplate of the motor it should have a kV-A locked rotor code letter.

This is used to estimate the starting current the motor uses, since when power is first applied it is at locked rotor (not-turning) conditions.

Tge full load current is in table 430.248.

A 1 HP motor on 115 V is 16 amps, and on 230 V is 8.0 amps.

Table 430.7 is the locked rotor code letter table.
It gives kV-A per horsepower.

The lowest value is 0-3.14 kV-A per horsepower, or 27.3 amps on 115 V, and 13.7 amps on 230 V.

Motor circuits do not follow the same rules as general purpose branch circuits, but a different set of rules in Article 430.

    Bookmark   May 7, 2012 at 12:30PM
Thank you for reporting this comment. Undo
Ron Natalie

The current demands to run the motor are roughly half at 240 than at 120. Less current for a given wire size means less voltage drop. Voltage drop can be a problem (can't say if it is in this situation). If you're going to run a new circuit, I'd certainly put in 240. It will be more flexible in the long run.

    Bookmark   May 7, 2012 at 4:08PM
Sign Up to comment
More Discussions
electrical outlet distance to radiator
how far from a radiator should a wall electrical outlet...
amsayan
Too much load for circuit?
I have 200 amp service to the main panel (which has...
zver11
new wiring project
I have a water damaged room I will soon be renovating....
CharlesInVT
A/C wired to main panel only?
I had 2 electricians come out to bid upgrading my service...
frank_diy
Crawl Space Junction Boxes: inspection and capping
Hello. I'm in the process of crawl space improvement....
SparklingWater
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™