Can any type wire (speaker or cable) be used in new construction?

johnfrwhippleMay 31, 2010

I had inspections two months back and my inspector made me pull out my speaker wire. Can he do this? Why?

He said that it didn't have any approvals or FT stamps or markings.

What is a FT stamp??? I live here in North Vancouver and have insured I pulled all proper permits.

Why do I need this. I bought the wire at my "Box" - it must meet code right?

How could wire with no FT rating even be sold if it's needed.

I'm so confused - please help..

The inspector went on to say that a fire starting in the living room could spread through out the whole house depending on the type of wire, it's burn rate and the path the wire takes through the home.

Scary. If that's the reason then for sure I would think this wire doesn't burn.

Does it?

I'll test them all - this week.

Thank you for reporting this comment. Undo
petey_racer

"Why do I need this. I bought the wire at my "Box" - it must meet code right?"

HAHAHAHA
Sorry, this made me laugh the moment I read it.

OK, seriously.

"Meet code"? What code?
Cable and wire are manufactured to a certain specification. THAT is meeting code. How you install it is another thing entirely. You can install perfectly legal and safe cable in a dangerous and non-complaint way.

I am not familiar with Canadian code on this so I cannot comment on the cable designations.

    Bookmark   May 31, 2010 at 11:29AM
Thank you for reporting this comment. Undo
mixman1

There are also specific cables that are "in-wall" rated. It has something to do with how the jacket of the cable reacts if the wire heats up due to excess current.

btw.....I am no professional, just read a lot of crap on the internet......

    Bookmark   May 31, 2010 at 12:40PM
Thank you for reporting this comment. Undo
netlos

the cable must be marked FT-4 on it to be "in-wall",by code.

    Bookmark   May 31, 2010 at 3:01PM
Thank you for reporting this comment. Undo
yosemitebill

Not sure on the exact equivalent of CSA (Canadian Standards Association) FT-4 but I believe it is CL2 or CL3 - riser rated.

Basically, what it comes down to is that if a fire was to start at or near the in-wall cable, would the cable contribute to the fire spreading? With the correct insulation, as in in-wall rated, it would not substantially contribute. Between floors, in vertical walls, it should be riser rated. If the cable passes through air handling areas (very unlikely in residential) it must be plenum rated as well which means the fumes emitted are within specific toxic limits.

The silver/gold zip-cord type of speaker wire is hardly ever in-wall rated... but the good thing is that the proper in-wall speaker cable (CL2/CL3) is usually cheaper.

Coax, Video, Audio, Ethernet cables all must be in-wall rated as well.

    Bookmark   May 31, 2010 at 5:56PM
Sign Up to comment
More Discussions
Badly done multi-wire circuits (previous owner strikes again..)
I bought a 1940-ish house last year, for which the...
quahog
Power to shed
Looking to run one 20 amp circuit to my shed and I'm...
ohio45424
Inspection Report
Had a gorgeous 1909 house inspected yesterday and don't...
cmae17
2 Lights Out on 4 Light Fixture
I was sitting at my dining room table, heard a tiny...
Cassandra
Two fans on same circuit in different rooms, can't get wiring right
So here's the situation. I have two ceiling fan/lights...
jenfarino
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™