Running electrical for spa

gabster7May 1, 2010

I am running electrical for a spa which will sit on the first level of my deck that is approximately 8" off the ground. My question is can I run my wires in solid conduit attached to the deck joists, and pop it up through the deck into a watertight junction box inside the access panel?

Thank you for reporting this comment. Undo
Ron Natalie

First off, I am of the definite opinion that spas and pools and other bodies of water you are going to allow your and your loved ones bodies to be immersed in is NOT THE TIME FOR AMATEUR HOUR. If you don't know Art. 680 well enough, you shouldn't be doing it.

The biggest problem with running the conduit directly into the spa is that would imply the lack of the proper maintenance disconnect. The home centers sell a $100 disconnect box that holds a 50 or 60A GFCI breaker inside it. You'll find that often ends up being a cheaper and more convenient solution.

    Bookmark   May 1, 2010 at 7:36AM
Thank you for reporting this comment. Undo
gabster7

Im sorry I didn't mention that I do have a 50 Amp GFCI spa disconnect panel mounted on the back of the house 10' away from and within sight of the spa. The run I was asking about was from the disconnect box to the spa, since the disconnect box needs to be at least 5' away from the spa. 10' per my local code. As my deck butts up to the house, I would run solid conduit down the wall from the spa disconnect box through the deck and along the joist to the spa. My question was really about whether or not I can run the conduit along the joist since it is so low to the ground or if I need to remove some of the decking and bury the conduit which will be no easy task.

    Bookmark   May 2, 2010 at 3:00AM
Thank you for reporting this comment. Undo
Ron Natalie

The disconnect does NOT need to be five feet from the spa. I can't vouch for local codes. The maintenance disconnect needs to be within sight of the person working on the equipment. The thing that needs to be five feet away is the EMERGENCY STOP for the motors. This, as far as the NEC is concerned, is not a requirement for single family home spa installations. Depending on what sort of stop you use, it may or may not qualify as the disconnect (or vice versa).

As for the conduit, you can run it as you describe. If it's exposed to sunlight, make sure you get something rated for such. I'd run wet rated conductors in it though.

    Bookmark   May 2, 2010 at 8:35AM
Thank you for reporting this comment. Undo
zl700

The best bet is use liquid seal-tite (outdoor flex conduit) and adapt to ridgid for any penetrations.

    Bookmark   May 2, 2010 at 11:55AM
Sign Up to comment
More Discussions
Does a refrigerator need to be on a separate circuit?
Does a refrigerator need to be on a separate circuit?...
rontero
new wiring project
I have a water damaged room I will soon be renovating....
CharlesInVT
Re-wiring range to service spa
what connectors are appropriate for joining 6-3 NMB...
justsomeotherdude
Crawl Space Junction Boxes: inspection and capping
Hello. I'm in the process of crawl space improvement....
SparklingWater
Light boxes on/in 6X8 timber floor joists for log home
Just trying to figure how to wire a couple light fixtures/chandelier...
yota_85
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™