Electrical Outlet Near Toilet Supply

dw85745April 10, 2013

I've moved the toilet and the toilet H20 supply is now in
the same wall cavity as an existing bedroom outlet which has
Romex 14-2 in it (Not GFI).

The outlet box is about 8 inches above the top of the H20 supply line. While no leaks are anticipated Murphy's Law is always an issue.

Does the NEC require this outlet to be GFI?

Thank you for reporting this comment. Undo
Ron Natalie

There's no code issue with the water pipes sharing a wall cavity with a box or NM cable. GFCI is not required here (in fact, last few revisions of the code mandate AFCI here).

What you can't do is make a receptacle on that circuit available for the bathroom. Bathroom receptacles have specific requirements (dedicated 20A circuits, GFCI) not met here.

    Bookmark   April 11, 2013 at 1:30AM
Thank you for reporting this comment. Undo
Ron Natalie

There's no code issue with the water pipes sharing a wall cavity with a box or NM cable. GFCI is not required here (in fact, last few revisions of the code mandate AFCI here).

What you can't do is make a receptacle on that circuit available for the bathroom. Bathroom receptacles have specific requirements (dedicated 20A circuits, GFCI) not met here.

    Bookmark   April 11, 2013 at 1:32AM
Thank you for reporting this comment. Undo
dw85745

ronnatalie: Thanks for response.

[quote]
What you can't do is make a receptacle on that circuit available for the bathroom. Bathroom receptacles have specific requirements (dedicated 20A circuits, GFCI) not met here.
[/quote]

Will leave as is -- but if GFI was required was going to power the bedroom receptacle from the bathroom circuit (which is 20A, UF, and GFCI).

Re: AFCI,: Was aware of this fact, Had thought about it, but would require an additional panel or major panel reworkl. Wiring all Romex and in great shape and I believe AFCI only required for new.

    Bookmark   April 11, 2013 at 9:20AM
Thank you for reporting this comment. Undo
brickeyee

"I believe AFCI only required for new."

It depends on how the AHJ views adding a new receptacle/outlet on a circuit.

They could require it to be AFCI protected.

It is just a breaker change in newer panels.

This post was edited by brickeyee on Thu, Apr 11, 13 at 16:03

    Bookmark   April 11, 2013 at 1:01PM
Thank you for reporting this comment. Undo
Ron Natalie

I don't think he's working on the electrical at all but the plumbing. You don't need to do anything strictly (unless he has some bizzaro building inspectors).

You can not connect things to bathroom receptacles willy nilly. Having a bedroom and bathroom receptacle on the same circuit is RIGHT OUT for a number of reasons.

    Bookmark   April 12, 2013 at 9:08AM
Thank you for reporting this comment. Undo
Ron Natalie

To be specific, let us use the term recepticle and outlet appropriately.

The receptacles (120V 15 or 20A) in the bathroom ALWAYS must be GFCI.

The receptacles in the bathroom can EITHER:

be on a 20A circuit that serves only outlets in that bathroom (i.e., outlets include lights and fans, etc).

-OR-
be on a 20A circuit that serves only RECEPTACLES in (more than one) bathroom.

An outlet in the bedroom or a non-receptacle outlet on a circuit serving multiple bathrooms is NOT allowed.

    Bookmark   April 12, 2013 at 5:13PM
Thank you for reporting this comment. Undo
hexus

"It is just a breaker change in newer panels."

not if it's a MWBC.

    Bookmark   April 12, 2013 at 7:48PM
Sign Up to comment
More Discussions
Re-wiring range to service spa
what connectors are appropriate for joining 6-3 NMB...
justsomeotherdude
How to get garage freezer to work in cold weather
I have a 7-year-old GE refrigerator/freezer in my unheated,...
amyf5
Need help with a rocker switch
I need to replace it in our SunHeat radiant room heater....
bold_as_love
Reuse electrical panel
I replaced a 24 circuit Square D panel with a new 40...
zver11
Light boxes on/in 6X8 timber floor joists for log home
Just trying to figure how to wire a couple light fixtures/chandelier...
yota_85
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™