GFI challenge

tim45z10April 28, 2010

I'm installing a GFI I'm putting two wires on the load side. One wire is slightly smaller than the other. When I screw the tightener, I cant get a grip on the smaller wire. Looking for ideas. Thank You.

Thank you for reporting this comment. Undo
secreto

Just use a wire nut that support three wires. Wire nut the two main wires with a short pig tail then wire to the one side of the GFI.

    Bookmark   April 29, 2010 at 12:31AM
Thank you for reporting this comment. Undo
hexus

the more important question is why do you have two different gauges of wires on the same circuit?

do you have 12 and 14 AWG on the same circuit? If so what size breaker is protecting this circuit? If it's not 15 then you have a bigger issue you need to address.

    Bookmark   April 29, 2010 at 1:07AM
Thank you for reporting this comment. Undo
tim45z10

One is the wire from the original build, 50 years ago. The other is new. I am going to see if I have enough room for a pigtail.

    Bookmark   April 29, 2010 at 2:33AM
Thank you for reporting this comment. Undo
bus_driver

I am not aware that wire gauges in use today are any different from that of 50 years ago. I was involved in the trade at that time. I have every NEC including 1959 and since. I need more information before offering advice.

    Bookmark   April 29, 2010 at 5:54PM
Thank you for reporting this comment. Undo
petey_racer

"One is the wire from the original build, 50 years ago."

But you have the breaker sized for the smaller wire, right?
Which would also mean it was a waste to run the bigger wire.
Which also probably means you have a violation by not having a 20A circuit in a bathroom or kitchen. Unless of course this is a different area.

I personally don't like the sound of this whole thing.

    Bookmark   April 29, 2010 at 8:00PM
Thank you for reporting this comment. Undo
hexus

must be that kind of wire we used to use back in the day that shrinks with age....

do the right thing, check into it please and don't just slap on the GFI and call it good. Is your house and safety really worth the risk?

    Bookmark   April 29, 2010 at 8:58PM
Thank you for reporting this comment. Undo
tim45z10

The difference is only .010-.015. Thanks for the suggestions. I pigtailed it and have completed the project.

    Bookmark   April 30, 2010 at 1:26AM
Thank you for reporting this comment. Undo
brickeyee

"The difference is only .010-.015."

Wire diameter?

The difference is than #14 is only rated for 15 amps, while #12 is rated for 20 amps.

But hey, at least you are insured by your homeowner's policy against your own mistakes.

    Bookmark   April 30, 2010 at 12:09PM
Thank you for reporting this comment. Undo
tim45z10

I am not a rookie. I know the difference between 12 and 14 just like you do. So stop with the rash remarks. I dont need them.

    Bookmark   April 30, 2010 at 1:16PM
Thank you for reporting this comment. Undo
Billl

Obviously you've found out how to make it work. I think the concern is that if you have 14 gauge wire in the circuit, you should verify that the breaker is only 15A. It isn't a problem you are causing with your fix, but it is a potential problem you uncovered and you should address it. Adding a GFI has made the situation slightly safer than it was, but that is no reason to ignore a possible fire hazard.

In the bigger picture, if you see something like that in a house, it should make you suspicious of all the other electrical work the prior owners did.

    Bookmark   April 30, 2010 at 2:02PM
Sign Up to comment
More Discussions
1 of 2 security light bulbs keep going out, do i need a new light?
I have a security light fixture in my carport that...
tlbean2004
Please Critique Low-Volt (Home Automation) Plan/Proposal
GW/Houzz Community, As always, I want to thank this...
Andrew K.
Badly done multi-wire circuits (previous owner strikes again..)
I bought a 1940-ish house last year, for which the...
quahog
Power to shed
Looking to run one 20 amp circuit to my shed and I'm...
ohio45424
Wiring in a 1 1/2" thick wall cavity
I need to run 12/2 wire thru an existing thin wall....
baker1mich
Sponsored Products
Underlayments: Custom Building Products Flooring SpiderWeb 54 sq. ft.
$84.97 | Home Depot
Sliding Pet Gate Dog Gate
$399.00 | FRONTGATE
Free Standing Cabinets Racks & Shelves: Keter Garage Cabinets Wide XL 35 in. x
Home Depot
Kartell | Joe Colombo Armchair
YLighting
ENO SingleNest Hammock by Eagles Nest Outfitters - SH004
$59.95 | Hayneedle
Electrical Tool Accessories: CabLED 18-Watt Indoor/Outdoor Power Supply 180-A241
$39.97 | Home Depot
Designers Edge L104 26-Watt Fluorescent Dusk to Dawn Flood Light with Acrylic Le
$49.99 | Hayneedle
Green Lunch Plus-to-Go Container
$5.99 | zulily
© 2015 Houzz Inc. Houzz® The new way to design your home™