Subpanel Issues

gellerApril 25, 2012

I just ordered some electric snow-melting cable that requires 40A/220V GFCI protection.

We have 200A service to our main panel, and there is only one slot left open. We have two C-H subpanels: one (fed by an 80A breaker) was recently installed for a renovation, and the other is older and fed by a 70A breaker. The older one only has 6 breakers in it, and only feeds our 3 A/C units.

So I thought, no problem, I'll put the 40A two-pole breaker in the subpanel for the A/C, since they will never be used at the same time, and the cover has 5 slots/side. However, I take the cover off and the buss does not extend beyond the existing 3 breakers/side. So I wonder if there is a way I can just install a longer buss in the case to accommodate the new breakers, since the case cover can cover 10 breakers (5/side). Of course, then I wonder if there is something in the NEC about what size feed I would need to accommodate more breakers (even though we will not exceed the 70A feed.

There is plenty of space in the newer subpanel, so that is another option: I could put the new double-pole breaker in there, but then would I need to worry about having a 35A load on one circuit when the whole subpanel is 80A? Yet another option is moving one circuit from the main box to the new subpanel, thereby opening up room for the new two-pole breaker (which would be SquareD rather than C-H).

Any advice is appreciated.

Thank you for reporting this comment. Undo
brickeyee

"I can just install a longer buss in the case "

Probably cheaper to replace the whole panel.

Panel parts are at a premium cost.

A larger cutout box with bus is very likely to be less than the parts (especially since it is likely to be a special order).

    Bookmark   April 26, 2012 at 10:38AM
Thank you for reporting this comment. Undo
geller

Thanks, brickeyee. Not clear if you thought the other options (moving a circuit from the main box) or putting the breakers in the newer subpanel were not practical.

    Bookmark   April 26, 2012 at 12:58PM
Thank you for reporting this comment. Undo
brickeyee

"would I need to worry about having a 35A load on one circuit when the whole subpanel is 80A?"

That depends on what the other loads on the panel are.

Load diversity, as you planned on using with the AC panel, might still be in your favor.
Few circuits are loaded to their ratings anyway and loading past 80% is generally prohibited, but even that depends on the type of load.

Few loads are long term 100% outside of resistive heating.

You also need to use the actual loads, not just the ratings on the breakers.

Adding up breakers means nothing.

    Bookmark   April 26, 2012 at 3:44PM
Sign Up to comment
More Discussions
Reuse electrical panel
I replaced a 24 circuit Square D panel with a new 40...
zver11
Replacing dimmer switch: different wire colors on new switch
My DR lights, which are controlled from two switches,...
msa6
Lights Flickering...
We paid an electrician to put in a ceiling light in...
regina_phalange
Looking for Ideas For Lighting at base of 300' long driveway
Sorry for the "picture through the screen"...
dixieman
Too much load for circuit?
I have 200 amp service to the main panel (which has...
zver11
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™