Central AC disconnect question

scottysApril 1, 2010

I need to replace a leaky, rusted ac disconnect switch before the warm weather arrives.

The question is: Currently have a 30amp non-fused model. All replacements I've seen so far are rated as 60amp.....the circuit breaker which feeds the ac in my main panel is 30 amp. Would installing a 60amp replacement disconnect cause any harm to the ac unit (or my wiring)?

Thank you for reporting this comment. Undo
brickeyee

Using a larger size disconnect is fine and will have no affect on anything.

    Bookmark   April 1, 2010 at 8:19PM
Thank you for reporting this comment. Undo
jcw48

You will find that a 60amp disconnect uses the large fuses that are only available in 40amp and above, although you can use the smaller fuses with a reducer.
30 amp disconnects are not uncommon and should be available any big box store.

    Bookmark   April 2, 2010 at 1:43PM
Thank you for reporting this comment. Undo
brickeyee

There is no reason to put any fuses in, but if that is the only disconnect readily available you can put any size fuse you want that is 30 amps or larger.

A couple of 60 amp fuses would be acceptable, as would a non-fused disconnect.

The CB is providing the over-current protection already.

    Bookmark   April 2, 2010 at 3:45PM
Thank you for reporting this comment. Undo
scottys

Thank you all for the replies.
I wound up getting a GE 60A non-fused disconnect.
The guy at the store said they no longer sell both 30 and 60 amp NON fuse disconnects because the box is really serving as nothing more than an on-off switch and that it is the circuit breaker in the panel which must be correctly sized....so BRICKEYEE you are right on the money. Thanks.

    Bookmark   April 3, 2010 at 8:33AM
Thank you for reporting this comment. Undo
brickeyee

There was a real lag by some of the condenser manufacturers in having their equipment listed for use with circuit breakers.

Thuisw meant that fuses were required to protect them (even when a circuit breaker was installed in the panel feeding them) and the disconnect was a simple place to put the fuses.

I have not seen any new equipment in the past 5-10 years that was not circuit breaker rated (And most residential breakers are also HACR allowing their use) so the requirement for a fuses has gone away.

Volume production lowers cost, and the price difference between a 30 amp and 60 amp is not enough to really justify the smaller device.

    Bookmark   April 3, 2010 at 11:41AM
Sign Up to comment
More Discussions
Disposer Power Cord
I recently bought a GE disposal online. The model is...
africanboy
Goodbye Phone Jack: what to do with wires?
We want to remove this phone jack. It's in a useless...
maggiepatty
2 Lights Out on 4 Light Fixture
I was sitting at my dining room table, heard a tiny...
Cassandra
Troubleshooting Kohler 12RES Problem
I have a Kohler 12RES generator with an RDT 100 Amp...
sniffdog
Confused & need help please
I know just about zero when it comes to electricity....
bicyclegirl1
© 2015 Houzz Inc. Houzz® The new way to design your home™