100 amp Service and fuses

robertz6April 3, 2013

I have a 100 amp service with fuses. Have read a couple of the threads about fuses.

Is it a hard and fast rule that a 100 amp service should use only 15 amp fuses, or can there be a few 20 amp fuses if the wires support 20 amps?

Thank you for reporting this comment. Undo
greg_2010

Is it a hard and fast rule that a 100 amp service should use only 15 amp fuses

Not only is it not hard and fast, it isn't even a rule at all. Where did you hear that? You probably have a bunch of circuits that aren't 15 amps. For example, water heater, dryer, etc.

If the wiring can support it, there's nothing wrong with using 20 amp fuses. You just can't switch out 15 amp fuses with 20 amp fuses without being sure that ALL of the wiring on that circuit is able to handle 20 amps.

    Bookmark   April 3, 2013 at 4:18PM
Thank you for reporting this comment. Undo
brickeyee

A 100 amp service is old, when not many electrical loads had even been considered, though I had a house once that had a meter with 30 amp contact ratings.
It still had 240 V though.

You can still load it up with any size branch circuits you need (up to the 100 A limit of course).

A huge arc welder, electric tankless water heater, or other special loads might be a problem.

An actual load calculation will tell you when you are getting close.

Keep in mind the sum of the branch circuit ratings in your case the sum of the separate fuses) does NOT indicate the actual load present.

Many a 200 amp panel has well over 200 amps of branch circuits installed.

'Load diversity' means that not all the branch circuits are pulling there rated capacity at the same time.

This post was edited by brickeyee on Thu, Apr 4, 13 at 13:36

    Bookmark   April 4, 2013 at 1:33PM
Thank you for reporting this comment. Undo
jreagan_gw

The big downside to most 100A load centers is the limited number of slots. There are no 42 breaker 100A load centers.

    Bookmark   April 9, 2013 at 11:05PM
Sign Up to comment
More Discussions
ceiling fan, fan works but lights do not
I have 2 kids and one threw a toy that hit one of the...
katy_bug
Well this sucks
Just when you thought the idiot popup ads in the gardenweb...
Ron Natalie
ARGH! no boxes
Went over to my daughter's house to help them change...
Ron Natalie
Too much load for circuit?
I have 200 amp service to the main panel (which has...
zver11
Replacing fan speed dial back to standard toggle?
I am removing a ceiling fan and replacing it with a...
onkyokoi
© 2015 Houzz Inc. Houzz® The new way to design your home™