3- or 4-wire to 120v subpanel in unattached "garage"?

dcsullivansApril 22, 2013

Hi -

We have a storage shed about 100' feet from the house on our property. It has no power now, and i'd like to run some out there so that I can have a couple of flood lights, have an outlet for the weed wacker, the occasional portable saw, etc. I only need a 120v circuit at this time.

I plan to run 1 or 1.5" PVC conduit underground with either 3 or 4 THWN lines (neutral, ground, and either 1 or 2 hots.) I'm thinking of using #10 wire, not so much for the amperage capacity, but to limit voltage drop.

Since I only need 120v, I'm planning on leaving the second hot wire (red) capped off at each end. My thinking is that if I ever needed 240v, I'd be able to upgrade without any additional digging, pulling wire, rewiring, etc.

I'm thinking that I'll install a small subpanel in the shed, but connect only 1 side of the bus. The neutral and ground will be isolated from one another, and I'll install 2x 8' grounding rods outside the shed.

Any thoughts or comments on this plan?

In particular, any reason to connect up both hots to the panel right away, even though I only need two somewhat smaller circuits at this time?

Thanks
Matt

This post was edited by dcsullivans on Mon, Apr 22, 13 at 15:05

Thank you for reporting this comment. Undo
greg_2010

any reason to connect up both hots to the panel right away

Why would you not hook up both hots? You'll have done 99.9% of the work already, so why not hook it up?

    Bookmark   April 22, 2013 at 3:59PM
Thank you for reporting this comment. Undo
dcsullivans

No real reason, other than I have to have a double-pole ready to go at the main panel.

Things are already a little crowded in there, so I might have to do a little juggling.

    Bookmark   April 22, 2013 at 4:34PM
Thank you for reporting this comment. Undo
brickeyee

The newest NEC requires 4-wire feeds to separate building panels.

What year NEC is the AHJ using

it is NOT always the latest one.

There is a separate provision that allows a single circuit to feed a detached structure without any panel at all.

20 A is the max, and GFCI protection is required on the feed.

A mutliwire circuit is a 'single circuit.'

This post was edited by brickeyee on Mon, Apr 22, 13 at 19:52

    Bookmark   April 22, 2013 at 7:49PM
Thank you for reporting this comment. Undo
dcsullivans

2005 NEC.

I'd rather run the 4-wire than do just the single circuit, even though that's probably all I need at the moment.

Thanks

    Bookmark   April 22, 2013 at 9:26PM
Sign Up to comment
More Discussions
new wiring project
I have a water damaged room I will soon be renovating....
CharlesInVT
A/C wired to main panel only?
I had 2 electricians come out to bid upgrading my service...
frank_diy
ceiling fan, fan works but lights do not
I have 2 kids and one threw a toy that hit one of the...
katy_bug
Too much load for circuit?
I have 200 amp service to the main panel (which has...
zver11
Multiple Fluorescent Ballasts in one light fixture
Hello GardenWeb. I'm not new here, but couldn't log...
MikeM21
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™