NorthlutApril 14, 2012

I'm looking at a fridge that has a "startup" rating of 20.1 amps, and a "running" rating of 3 amps. Does this need a 20 amp circuit, or is it ok on a normal household 15 amp circuit?

Thank you for reporting this comment. Undo
bus_driver

The 15 amp circuit will be OK. Brief overloads are tolerable. The maximum startup current is for fractions of a second.

    Bookmark   April 14, 2012 at 11:18AM