wiring 240v table saw to breaker panel

georgevancouverApril 28, 2014

I have a Delta 36-650 table saw set up for 240 v use. The motor is already configured for 240 use. Not sure how to hook it up to the breaker panel.
New breaker panel and new location.

Thank you for reporting this comment. Undo
Ron Natalie

Ah, the famous Delta Contractor's saw. I used one of those for decades before I got my SawStop cabinet saw.

That saw is designed to be cord and plug connected. Read the manual. It's designed to have a 15A 240 (6-15) Plug on it when you are using the 240V mode. I'd put in a 20A 240 Receptacle (6-20) which will accept the 6-15 plug but leaves your options open. I'd not put anything else on that circuit (at least nothing you'd tend to run at the same time as the saw).

    Bookmark   April 28, 2014 at 11:59AM
Thank you for reporting this comment. Undo
bcarlson78248

This diagram shows the shapes for each receptacle type.
http://www.stayonline.com/reference-nema-straight-blade.aspx

Assuming you have a standard panel and no need to use conduit to protect the wire:
Just run 12/3 NM wire from the 6-20 or 6-15 receptacle to a double breaker in the panel. Connect black and red wires to the breaker, and white and ground to the bus in the box. Follow the instructions that come with the receptacle to make sure its wired correctly. Make sure you shut off the main breaker when working in the box.

Bruce

    Bookmark   April 28, 2014 at 6:32PM
Thank you for reporting this comment. Undo
joefixit2

"and white and ground to the bus"

Why would you run a neutral to a 240 volt receptacle?

    Bookmark   April 28, 2014 at 11:35PM
Thank you for reporting this comment. Undo
Ron Natalie

As I stated, this saw only requires a 6-15 (2 hots and a ground) which is what is shown in the manual. There's no need for a neutral (nor any place to connect it on that receptacle). In some cases I might run a neutral to the box just in case I needed to hook up a four wire circuit in the future, but here I wouldn't. I have four 240V receptacles in my shop running a larger table saw than this, a dust collector, an air compressor, and a jointer/planer. None of them needs a neutral. 12/2 would be fine here.
There's no place to connect that white wire not he 6-20 receptacle.

It is not the case that you connect the grounded (white) and the ground (bare/green) to the same bus. This only can happen at the service disconnect. The suggestion of a new panel indicates this MIGHT not be the service disconnect but rather a sub panel.

Further, you can not put a single 15A receptacle on a 20A breaker.

There's neither a requirement to shut off the main breaker (if there even is one) nor does shutting off the main breaker reenergize everything in the panel. If you don't know what you need to do to work safely in the panel, you should have an electrician come in to do the work.

    Bookmark   April 29, 2014 at 8:45AM
Thank you for reporting this comment. Undo
jimct01

If the receptacle,contains two outlets, you can use it on a 20 amp circuit. If it's a single and ther no other outlets on he circuit then you must use a 20 amp receptacle.

    Bookmark   May 14, 2014 at 9:25PM
Thank you for reporting this comment. Undo
rwiegand

Putting the outlet on a nearby wall switch (double pole to disconnect both legs) makes it convenient to kill power to the saw when changing blades and such. While it would be hard to do I could imagine leaning on the switch on my PM66 and turning it on inadvertently. Rather not do that while handling the blade.

    Bookmark   May 15, 2014 at 2:06PM
Thank you for reporting this comment. Undo
Ron Natalie

That's why the cord conveniently comes out of the wall (it can serve as a disconnect), but an appropriately rated switch will work as well.

    Bookmark   May 15, 2014 at 7:41PM
Thank you for reporting this comment. Undo
rwiegand

My cord comes conveniently out underneath the saw, where I don't trip over it while working. However I have to get on my hands and knees to unplug it, making it a less-likely-to-be-used disconnect.

    Bookmark   May 19, 2014 at 12:04PM
Sign Up to comment
More Discussions
Testing a fluorescent bulb
I've got a light box that isn't lighting up when I...
kudzu9
Inspection Report
Had a gorgeous 1909 house inspected yesterday and don't...
cmae17
Wiring in a 1 1/2" thick wall cavity
I need to run 12/2 wire thru an existing thin wall....
baker1mich
Need to Understand GFCI Requirements.
I posted this in the remodeling section, but I think...
homechef59
Subpanel Question
I have a 100 amp panel being fed by #4 awg copper wire I...
Calo Renovations
Sponsored Products
Armen Living Igloo Counter Stool - LCIGBAVIBR26
$249.30 | Hayneedle
West 12th Table Lamp by SONNEMAN Lighting
$430.00 | Lumens
Goa Cutlery - 5pcs - Cutipol
$63.00 | HORNE
Century Silver Eight-Light Clear Heritage Handcut Crystal Chandelier, 24W x 21.5
Bellacor
Zuo Bang Mirror
Beyond Stores
5-Pc. Poolside Lounge Set in Coffee/Turquoise
Dot & Bo
© 2015 Houzz Inc. Houzz® The new way to design your home™