GFCI breaker

eddie2626April 23, 2013

I'm trying to installation GFCI breaker. I cannot determine which is the ground wire.I followed the load wire to the top of the breaker box and there is no white wire in the same conduit pipe. the wall is finished so I cannot follow the power wire out of the box .
How can I find the ground wire?

Thank you for reporting this comment. Undo
Ron Natalie

You need professional help.

A white wire is never a ground wire. The ground wire is either bare or green. If this conduit is metal, it may be legally serving as the ground.

The grounded conductor (commonly called neutral) is white.

Is this a 240V circuit by any chance? In that case there may indeed be no (white) neutral.

The ground doesn't get connected to a GFCI breaker so I'm not sure why you are worried about it.

    Bookmark   April 23, 2013 at 8:45AM
Thank you for reporting this comment. Undo
bus_driver

Many posts here recently have been from those who registered that day and then posted nonsense. I think we have a really creative prankster trolling here. I'm going to scale back my efforts for a while.

    Bookmark   April 23, 2013 at 5:26PM
Thank you for reporting this comment. Undo
btharmy

Judging by the bad grammar, I can only guess who it might be. Hmmmmm, I wonder.

    Bookmark   April 24, 2013 at 4:05PM
Sign Up to comment
More Discussions
Grounding Service panel 200amp
Is the new NEC saying to no longer run # 4 copper wire...
36066
Outdoor subpanel as AC disconnect
Can we use an outdoor subpanel as an AC disconnect?...
ylmzm
Need to Understand GFCI Requirements.
I posted this in the remodeling section, but I think...
homechef59
Dryer power cord next to vent
My contractor is enlarging the dryer vent hole in the...
phil2015
Troubleshooting Kohler 12RES Problem
I have a Kohler 12RES generator with an RDT 100 Amp...
sniffdog
Sponsored Products
Progress Lighting 300-Watt Landscape Lighting Transformer P8654-31
Home Depot
TL550 480W Remote Magnetic Transformer
Lightology
Kidwise Princess Party Bounce House - KWWS-MP-1001
$489.00 | Hayneedle
Kichler Manual Series 100-Watt Bronze Transformer
Lamps Plus
Monorail 2-Circuit 2x250W Sloped Surface Mount Transformer
Lightology
Men's Rashguard
$39.50 | FRONTGATE
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™