Replacing outlet with GFCI outlet

nmtinxApril 29, 2014

Dear all,

I tried to replace a 20-year old outlet with GFCI outlet under my kitchen sink. The outlet used for the disposal and dishwasher. After I took the old one out and I found there 3 wires - red, orange and white. For the other outlet, usually it only comes with red and white for the line wires. I just wonder what is the orange wire used for? where should I hook into in my GFCI outlet? should I hook that up as a load wire? but how come that only come with 1 white not 2 white wires?

Thanks.

Thank you for reporting this comment. Undo
joefixit2

The receptacle is split wired for a dishwasher and a disposal, a GFCI receptacle won't work there. Why do you want a GFCI there anyway?

    Bookmark   April 29, 2014 at 12:25AM
Thank you for reporting this comment. Undo
nmtinx

Thank you for your reply. I replace it since it is my rental unit My town has a new regulation for rental unit. Any outlet within 6 feet of kitchen sink needs to replaced by GFCI outlet. Since the outlet is right under the sink so I have to replace it with GFCI. I just wonder how can I fix that if GFCI receptacle won't work there?

Thanks again

    Bookmark   April 29, 2014 at 9:21AM
Thank you for reporting this comment. Undo
greg_2010

Any work on a rental unit must be done by a licensed professional.

That said, are you sure that it's ALL receptacles? Or just general-use countertop receptacles?

    Bookmark   April 29, 2014 at 10:04AM
Thank you for reporting this comment. Undo
weedmeister

What you're looking at is two circuits on the same receptacle. One for the DW, one for the GD. This can be done with a single receptacle by breaking off a tab that is normally between the two screw terminals, missing in this photo.

    Bookmark   April 29, 2014 at 9:44PM
Thank you for reporting this comment. Undo
pittsbfan200

I just had the same setup. What I would do is put a wire nut on the red or orange, whichever one is switched. Then I would install the GFCI receptacle. Then I purchased the following from garbage disposal switch from amazon - http://www.amazon.com/InSinkErator-STS-SO-Single-Outlet-Buttons/dp/B001DELK2Y/ref=sr_1_1?ie=UTF8&qid=1399472279&sr=8-1&keywords=garbage+disposal+switch

It did require me to put a hole in my sink since I did not have any extras.... It works great... You could then remove the switch - put a wire nut on the end and tape it good. then put a blank in there.

You could always replace the breaker with a GFCI breaker.

    Bookmark   May 7, 2014 at 10:24AM
Thank you for reporting this comment. Undo
human321

Not sure I follow this post completely. As has been stated you have two circuits sharing a common neutral on a duplex receptacle. I do not believe this is required of GFCI as it always has something plugged in it and
it is below sink. I hope you have both circuits off as you are working on this as those that do not understand splitting of a receptacle is very dangerous.

    Bookmark   May 27, 2014 at 12:14AM
Thank you for reporting this comment. Undo
Ron Natalie

There is nothing in the US codes that cover "things always plugged in." If it is in a place that requires a GFCI and it is a 15A or 20A 120V receptacle it needs a GFCI. However, as far as the national codes go, under the sink, is not one of the places requiring a GFCI.

    Bookmark   May 27, 2014 at 8:32AM
Thank you for reporting this comment. Undo
joefixit2

"as far as the national codes go, under the sink, is not one of the places requiring a GFCI"

Actually it is for 2014. See 210.8 (D)

This post was edited by joefixit2 on Tue, May 27, 14 at 22:00

    Bookmark   May 27, 2014 at 9:54PM
Thank you for reporting this comment. Undo
jreagan_gw

210.8(D) is for dishwashers. Garbage disposals are picked up by the removal of the phrase "located in areas other than kitchens" from 210.8(A)(7). Most under the sink receptacles are within the "6ft from edge of sink" requirement and now require GFCI protection.

    Bookmark   May 28, 2014 at 12:19AM
Sign Up to comment
More Discussions
Troubleshooting Kohler 12RES Problem
I have a Kohler 12RES generator with an RDT 100 Amp...
sniffdog
Badly done multi-wire circuits (previous owner strikes again..)
I bought a 1940-ish house last year, for which the...
quahog
Humming Transformer
Last summer the POCO replaced the transformer on the...
mike_kaiser_gw
Subpanel Question
I have a 100 amp panel being fed by #4 awg copper wire I...
Calo Renovations
Confused & need help please
I know just about zero when it comes to electricity....
bicyclegirl1
Sponsored Products
Jamestowne Small Antique Brushed Nickel Outdoor Wall Lantern
$54.50 | Bellacor
MLB 12 x 15 in. Petco Park Stadium Plaque - 1215PETCO
$32.99 | Hayneedle
Moonrays Path & Landscape Lights Outdoor Black Low-Voltage 4-Watt 2-Tier Path
$7.99 | Home Depot
Rubber Tub Stopper, Chain and Overflow Bolt
Signature Hardware
E27 LED Decorative Bulb, Bent Tip Shape
Super Bright LEDs
MR11 LED Bulb, 12 LEDs
Super Bright LEDs
Elk Lighting Celina 3-Light Chandelier in Polished Chrome & White Swirl Glass
Beyond Stores
Modern Slim-Line 26 Inch Three-Light Pendant
$188.10 | Bellacor
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™