AFCI Problem update.

kingmerMarch 27, 2010

Update to AFCI problem....

So, I identified the receptacle that had the main run from room to main panel box, it had the one input from the main panel and two outgoing lines to each side of the room...(All three wire 12 gauge yellow jacket)

First step: Disconnect all but the main run to the one receptacle.....

1) Fantastic, it works, no tripping even under heavy ac motor load.

2) Hook up first branch....it works! even under heavy load....so the main run and one branch are A-OK.

3) Hook up second branch, put load, POP breaker opens.

4) Disconnect every receptacle in series then hook them up until failure...First receptacle...fine...second, POP under load!

5) The second receptacle branches twice more, disconnect

branches so only link between first and second receptacle...POP under load

Now the sad news, the connection between first and second receptacle on the problem branch is 12 gauge romex that travels at least 15 feet, up and over a door...

NOW WHAT!?!!?! I have identified the problem link, but man, how do i pull a new cable through? Tear out dry wall? Do I have any options here?

Thank you for reporting this comment. Undo
hendricus

First receptacle works fine and second pops the breaker.

Disconnect second receptacle but leave wire hooked to first receptacle that goes to second receptacle. Turn on juice to see if breaker still pops with line attached and second receptacle detached. Attach a load to the bare wires and see if that pops the breaker.

    Bookmark   March 27, 2010 at 10:36PM
Sign Up to comment
More Discussions
Light boxes on/in 6X8 timber floor joists for log home
Just trying to figure how to wire a couple light fixtures/chandelier...
yota_85
Replacing dimmer switch: different wire colors on new switch
My DR lights, which are controlled from two switches,...
msa6
Doorbell goes off by itself.
Can anyone tell me why this would happen? It's a wired...
stu2900
Too much load for circuit?
I have 200 amp service to the main panel (which has...
zver11
A/C wired to main panel only?
I had 2 electricians come out to bid upgrading my service...
frank_diy
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™