Roman RytovMarch 19, 2008

I'm about to tile my kitchen floor (slab, engineered hardwood) and before doing that want to add two sockets to the island in the middle of the kitchen (no sink, no oven).

So the question is do I put romax cable in a protecting hose (forgot the right name for that) or just place it under tile into cement?

Thank you for reporting this comment. Undo
spencer_electrician

You won't be using romex at all. Under the floor on a slab is considered outdoors and will require wet rated wire. This would be thwn individual black, green, and white wires through pvc or metal conduit. The conduit will have to run from the box on the island to a source box from the kitchen wall (conduit complete). If running a complete conduit is inconvenient, you may be able to use UF (outdoor romex) but it still needs to be sleeved with conduit with a stub up at the island and the other end where it then is just the UF romex again.

    Bookmark   March 19, 2008 at 11:23PM
Thank you for reporting this comment. Undo
Roman Rytov

maybe I explained it not in enough details. On the slab I have glued engineered hardwood (1/2"), then I'm putting cement boards on thinset (so other 3/4"), and then tile it.

I thought to put the wires either between the boards, or even make a groove in the hardwood for the wires.

Does it still mean I have to use conduit under tiles and in the island?

    Bookmark   March 20, 2008 at 9:38AM
Thank you for reporting this comment. Undo
Ron Natalie

Not withstanding the electrical problems, this sounds like a flooring disaster waiting to happen. You might want to run this by in the flooring forum first.

You can't do what you want with the wiring (either suggestion).

The proper way to do this would be to remove the previous finish floor, cut a channel in the slab and install conduit.

    Bookmark   March 20, 2008 at 9:59AM
Thank you for reporting this comment. Undo
Roman Rytov

:-) thanks for pointing it out.

Why do you think I can't do it? the total thickness allows to put conduit even without cutting a channel in slab. why you think I should remove flooring for laying conduit?

    Bookmark   March 20, 2008 at 10:22AM
Thank you for reporting this comment. Undo
texasredhead

I presume, dangerous thing to do, you are getting a permit for the wiring. If so, I would run your ideas through your local inspection folks. There is also the possibility that a careless floorer might run a nail through it.

    Bookmark   March 20, 2008 at 1:28PM
Thank you for reporting this comment. Undo
heimert

It seems to me that if you can get the conduit fully under the cement board--in a channel between boards (whether you need to cut a channel or not) would be sufficient and won't create a flooring problem. The cement board will be able to span a 3/4" or 1" gap. If neecessary you could put some sort of filler around the conduit so there's no gap.

    Bookmark   March 20, 2008 at 3:05PM
Thank you for reporting this comment. Undo
jason1083

romanr: tile guys will not warm to this Idea well. Leaves a heck of joint to try and mud (you know the cement board joints must be mudded with thinset and akali resitant mesh tape and that thinset must be placed under the CBU?)

Heimert: cement board has no structural value assigned to it so it should not be bridging and gaps.

    Bookmark   March 20, 2008 at 3:10PM
Thank you for reporting this comment. Undo
live_wire_oak

The hardwood MUST be removed if you actually want your tile job to last beyond about 3 months and not be a waste of time and money. And, the slab MUST be channeled into in order to properly route electricity to the island. This isn't a job in which to cut corners.

    Bookmark   March 20, 2008 at 4:33PM
Thank you for reporting this comment. Undo
Roman Rytov

I heard the opinion that hardwood must be removed. Although an alternative option was backed up by a few contractors. The logic for leaving the hardwood was:
- it's glued, not floating or nailed so not moving;
- in this fashion it's similar to plywood floor;
- screwed hardboards (and two thinsets) will secure tiles from potential hardwood deformations;

Does it sound logical or you think deformations/movements can be so strong that they will go through the cement hardboards and push tiles?

    Bookmark   March 20, 2008 at 8:09PM
Thank you for reporting this comment. Undo
jason1083

The problem is it does not have the same strength as plywood plus plywood used in a tile job must have an exposure 1 rating meaning outdoor adhesive is used in its manufacture. On the flooring forum look for a guy named bill Vincent, he is an experienced tile setter.

IF I did tile over hardwood I would likely use an uncoupling membrane such as ditra.

    Bookmark   March 21, 2008 at 3:25AM
Sign Up to comment
More Discussions
Looking for Ideas For Lighting at base of 300' long driveway
Sorry for the "picture through the screen"...
dixieman
Reuse electrical panel
I replaced a 24 circuit Square D panel with a new 40...
zver11
Does a refrigerator need to be on a separate circuit?
Does a refrigerator need to be on a separate circuit?...
rontero
electrical outlet distance to radiator
how far from a radiator should a wall electrical outlet...
amsayan
ceiling fan, fan works but lights do not
I have 2 kids and one threw a toy that hit one of the...
katy_bug
© 2015 Houzz Inc. Houzz® The new way to design your home™