baseboard heater question

first_timerMarch 1, 2010

Hi all,

Our new house (actually new to us -- it was built in '85) has all 240V baseboard electric heat. While replacing a couple of the units, I noticed that I needed to shut off several seemingly unrelated circuits to completely shut off power to the heater and to the thermostat. It LOOKS like in all rooms, the heaters use 2 separate single-pole circuits each, one that seems dedicated to the heaters and one that is usually a general use circuit (with lights & receptacles). Is this common practice? is this safe for electronics like computers?

I noticed the lights dim when they heater kicks in.

What would fix this besides running new circuits?

Thanks

Thank you for reporting this comment. Undo
bus_driver

Only a knowledgeable workman doing an on-site inspection can determine if your observations are correct. The arrangement that you believe you have is not at all conventional. Sounds as if it might not be to code.

    Bookmark   March 1, 2010 at 6:36PM
Thank you for reporting this comment. Undo
Billl

Well, the house has presumably run like this for 25 years, so I wouldn't panic. However, that is not how you should wire a baseboard heater. It should be on a double pole breaker. That way, if anything goes wrong, both legs trip at once. In the current design, you've lost some of the protection that a circuit breaker is supposed to provide. You should upgrade the wiring as you are able to address this safety issue.

As for your electronics, you've got visual evidence that these circuits are not providing a consistent voltage to power anything on the dual use leg. You've also got some potential neutral/grounding issues depending on how the circuits are joined at the heaters. It is definitely a less than ideal operating environment for expensive electronics. They sell all sorts of surge protection/voltage regulating devices for electronics, but good ones aren't cheap.

    Bookmark   March 2, 2010 at 9:26AM
Thank you for reporting this comment. Undo
davidro1

I don't believe that you "... needed to shut off several seemingly unrelated circuits to completely shut off power to the heater and to the thermostat..." Your next sentence made it look like you needed to shut two.

Do a little more homework and post again. If you don't map out what is on which breaker, who will?

    Bookmark   March 2, 2010 at 11:56AM
Thank you for reporting this comment. Undo
first_timer

Thanks for the responses.

I think I'll call in my electrician and see if he can tell me what's going on.

It sounds a bit dodgy...

    Bookmark   March 2, 2010 at 3:37PM
Sign Up to comment
More Discussions
Grounding Service panel 200amp
Is the new NEC saying to no longer run # 4 copper wire...
36066
Troubleshooting Kohler 12RES Problem
I have a Kohler 12RES generator with an RDT 100 Amp...
sniffdog
Bath fan/light combo
Attached is wiring diagram of masterbath (I hope I...
jaspol
Can you make a splice inside one of these?
The reason I ask is my neighbor's house was destroyed...
schreibdave
Outdoor subpanel as AC disconnect
Can we use an outdoor subpanel as an AC disconnect?...
ylmzm
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™