Portable vs Standy Generators

weedmeisterMarch 20, 2013

I was wondering what the pros would have to say about the following question and response from a company that sells portable generators. I understand that there is a difference in the NEC when describing (and connecting) portable emergency generators versus fixed standby generators.

------------------
I'm a licensed NH Electrician I have a Honeywell 7500Watt Portable Generator that will be used to supply selected loads in a non-separately derived residential application as outlined by the 2011 NEC. The tag on this generator indicated that the neutral is bonded to the frame. I need to know if this generator can be made into a floating neutral generator without voiding listings or warranty. If the answer is yes then where and how does the manufacture recommend the removal of the bond? And will the manufacture send a new label that indicates the generator is now a floating neutral generator. This will be an issue with any generator that has its neutral bonded to the frame portable or stationary. Any info that you can give me will be a great help.

Regards,

Ron T.

by Ron T. from New Hampshire on January 08, 2012

A: The manufacturer does not recommend removing the bonded neutral from the generator and neither do I and just about 97% of generators on the market have a bonded neutral.

If you need to break the neutral in the generator backup set-up then you need to go with a GFI type transfer switch such as the Reliance Controls "X" series switches.

Note: Typically these switches are not required unless the large transfer switch outlet on the generator is GFI protected which is found on Professional generators such as the Generac "XP" models and not the "XG" model.

The biggest thing, is the fact that a generator has a bonded-neutral does not rule out compatibility with 2-pole transfer switches. The only time that a portable generator will not be compatible with a 2-pole transfer switch is if the generator has a bonded-neutral AND there is a GFCI breaker or GFCI mechanism protecting the receptacle they are using to connect the generator to the transfer switch.

Code does not require switching the neutral, so using a bonded generator with a Pro/Tran is perfectly fine as long as there is not a GFCI built into the receptacle that is being used. If there is a GFCI, it won't work because the breaker trips.

Any time a bonded-neutral generator is connected through a transfer switch to a house wiring system, there are two neutral-to-ground bond points: one at the main panel and one at the generator.

Having two bond points creates 'dual paths' on the ground and neutral, aka "ground loop", meaning the ground wire from the generator to the house panel will share everything with the neutral wire from the generator to the house panel.

This leads to there being a very small amount of current on the ground. If there is a GFCI breaker tied into the generator receptacle, it will sense this current on the ground and trip every time the generator is connected, even under No load.

* If the generator does not have a GFCI protecting the in-use receptacle, there will not be a trip and the generator will power circuits
successfully.

A common argument against this is: "but the ground cannot have any voltage or current in any situation" - this is not true. The NEC states "the ground cannot carry 'objectionable' current".

The ground wire in question is the wire between the house panel and the generator, a small amount of power on this wire is not a safety concern in this type of application.

We have no record of a single injury, or a single inspection ever turned down, related to a bonded neutral generator connected to a home through a 2-pole transfer switch.

Note that this has been done historically for decades, using bonded generators without switching the neutral, ever since generators and transfer switches existed.

There was never a problem until about 10 years ago when generators started adding GFCI's (per OSHA job site requirements) and wiring them into the larger receptacles. GFCI's on the 15 amp 120v outlets are usually separate and not connected to the 4 wire 120/240 outlets, but it's a challenge to identify this without contacting the manufacturer. It varies greatly and is rarely specified in the owners manual.

The entire problem here is related strictly to the GFCI breakers built into bonded-neutral generators, not the fact the generator has the neutral bond alone. In knowing this, if we look at all of the portable generators that are bonded neutral, and then if we separate the models WITH a GFCI breaker protecting the 120/240 outlet, the percentage of these generators is extremely small. These are the only generators that will ultimately require a 3-pole transfer switch that breaks the neutral.

Breaking the neutral simply eliminates the ground loop (dual paths) between the generator and house panel created by having two bond points, and will eliminate the problem of the GFCI breaker tripping.

I hope this information was helpful.
-----------------------------------

Thank you for reporting this comment. Undo
brickeyee

The bond should be removed if the generator will be connected to a panel that already has a ground-neutral bond.

If you have the panel and the generator both bonded the neutral current will be on both the ground and neutral conductors between the panel and the generator.

That means the generator's frame is NOT at ground potential (as it should be with a 4-wire connection to fed a 120/240 V panel in a structure).

Generator manufacturers typically call for an earth ground rod to be connected to the generator's frame.

I cannot remember the last time I saw anyone do this.

Your generator is NOT a 'required' source under the NEC, so it is not treated as one.

Emergency facilities (think hospital life safety), sprinkler system pump backup generators, etc. ARE often REQUIRED sources.

They may be allowed to run until destruction if a problem occurs.
Allowing the equipment to be damaged is not as important as maintaining power.

Think of it as a 'battle short' that is used on some pieces of ship mounted naval equipment.

They actually short out protective devices on equipment that MUST operate.

Your home backup generator is far more of convenience for most folks.

I have installed sets for quadriplegics on a ventilators that the AHJ agreed was "required."

The poor guy was in a rural area subject to prolonged power outages (days) that his UPS system & battery backup simply could not support.

The generator was a sort of belt and suspender thing.

    Bookmark   March 20, 2013 at 5:17PM
Sign Up to comment
More Discussions
Doorbell goes off by itself.
Can anyone tell me why this would happen? It's a wired...
stu2900
Well this sucks
Just when you thought the idiot popup ads in the gardenweb...
Ron Natalie
Crawl Space Junction Boxes: inspection and capping
Hello. I'm in the process of crawl space improvement....
SparklingWater
How to get garage freezer to work in cold weather
I have a 7-year-old GE refrigerator/freezer in my unheated,...
amyf5
Lights Flickering...
We paid an electrician to put in a ceiling light in...
regina_phalange
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™