Covered Patio GFI requirement

lwimMarch 28, 2011

Two questions:

1) We're in the final stages of adding a large 15x32 covered patio attached to our house. We have two 20 Amp circuits, one serving 2 outlets and the other 3 outlets, all located in the ceiling, about 12 feet off the floor. Their purpose is to be used for electric heaters. Nothing else are on the circuits. Do these require GFI protection? My electrician says they don't because they're not in a reachable location. Is this correct?

2) We have another cicuit that serves three fans with lights, rope lights and 8 can lights. There are no outlets on this circuit. Does it require a GFI breaker since it's outside?

Cheers,

Larry

Thank you for reporting this comment. Undo
Ron Natalie

1. If you're subject to the National Electrical Code he's wrong.
The code only permits the "not readily accessible" outdoor receptacles to be exempted from the requirement when they are to there to feed certain loads of which space heaters aren't one of them (the permitted rules are for snow melt/deice, and pipe/vessel heaters).

2. Receptacles must be protected. If the rope lights are plugged into a receptacle, then those need to be protected. Lighting and fans do not need GFCI protection unless the manufacturer requires it in the specifications. Some wet location units do have that requirement.

    Bookmark   March 28, 2011 at 4:44PM
Sign Up to comment
More Discussions
Insulation in electrical box
While in my attic the other day I saw an open electrical...
sgilliatt
Crawl Space Junction Boxes: inspection and capping
Hello. I'm in the process of crawl space improvement....
SparklingWater
Well this sucks
Just when you thought the idiot popup ads in the gardenweb...
Ron Natalie
ARGH! no boxes
Went over to my daughter's house to help them change...
Ron Natalie
Looking for Ideas For Lighting at base of 300' long driveway
Sorry for the "picture through the screen"...
dixieman
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™