Hot breaker

capmarineMarch 28, 2010

After an earthquake the sub panel in our guest house began to heat and the smell of smoke was present. I opened the breaker box and removed the breaker that was hot and noticed that sparks were comming from the nueteral buss and the only way I could stop the sparks was to pull all four breakers and then the box cooled down to normial. None of the breakers were thrown. When I tried to replace the breakers the same thing happened. Do I need to replace the breaker box? This is an old system that didn't use a ground, only the nuterial buss.

Thank you for reporting this comment. Undo
bigbird_1

"Do I need to replace the breaker box?"

Yes, ASAP, with a proper ground.

    Bookmark   March 28, 2010 at 6:40PM
Thank you for reporting this comment. Undo
pharkus

That's definitely an odd one. First things first, turn off the feeder to the subpanel, at the other end. You definitely have an unsafe condition.

After the power is off, check that all the neutral connections are tight. If one is absurdly loose, that may be your issue.

If that is NOT your issue, then please, DO NOT turn that panel back on until the true problem has been found and solved.

It may very well be that the panel itself is structurally damaged - although I'm having a tough time wrapping my head around how that would lead to sparks from the NEUTRAL bar.

I try not to give this answer, because it seems like a cop-out from helping people learn, but this is a pretty serious issue, and you really do need to call in someone who knows what they're doing. I DO believe in DIY, as long as there are forums like this to help, but when sparks and smoke are already involved, things become time-critical. Whatever the problem is could very well set the house on fire while you're waiting for us to reply!

So get that feeder turned off. NOW. Don't wait.

    Bookmark   March 28, 2010 at 6:45PM
Thank you for reporting this comment. Undo
groundrod

When would you consider calling a professional in, after the fire dept. has left?

    Bookmark   March 28, 2010 at 9:23PM
Sign Up to comment
More Discussions
Inspection Report
Had a gorgeous 1909 house inspected yesterday and don't...
cmae17
Disposer Power Cord
I recently bought a GE disposal online. The model is...
africanboy
2 Lights Out on 4 Light Fixture
I was sitting at my dining room table, heard a tiny...
Cassandra
Need to Understand GFCI Requirements.
I posted this in the remodeling section, but I think...
homechef59
Grounding Service panel 200amp
Is the new NEC saying to no longer run # 4 copper wire...
36066
Sponsored Products
DW 3528 Single Row LED Strip Light 240/m 10mm wide Foot
EnvironmentalLights.com
Mulled Apple Cider Set
$44.99 | Dot & Bo
Tec Pura Brass Chrome Plate Diverter Single Inlet 2, 3 Or 4 Outlets
Hudson Reed
Elnora Bridge Bathroom Faucet - Porcelain Lever Handles
Signature Hardware
Klus 1547 - LED Profile Lens, Standard Frosted
Super Bright LEDs
International Caravan Aluminum Tilt and Crank 8-foot Outdoor Umbrella
Overstock.com
© 2015 Houzz Inc. Houzz® The new way to design your home™