I'm installing two duplex recepticles in a two gang box. I'm feeding this from a home run to my GE breaker box. I'm using 14-3, multiwire curcuit.

From what I've learned, the newer NEC now requires a two pole C/B with the handle tie feature, even if each phase feeds one yoke? I've been looking for a GE THQP215, and could not easily find one. Home Despot didn't carry them where I am.

Note: Each duplex outlet will be fed from one leg, with pigtailed neutrals

Is the reason for the code change to ensure that each pole is fed from a different phase, or is it to protect someone working in the box?

Thank you for reporting this comment. Undo
bus_driver

Lots of two-pole breakers have just one handle, common-trip. The SqD QO series is one example. Since two circuits on opposite poles share a neutral, shutting off just one of those circuits leaves the other circuit energized. If the energized one is actually supplying some load and the neutral is opened at certain points, as one might do if working on the other circuit and believing that is not live, the open end of the neutral nearest the load of the still-energized circuit will then be energized at 120 volts. Nasty surprise- or worse. The common-trip or tied handles solves that problem.
Your store can order the breaker. Will they? Ask them.

Here is a link that might be useful: Breaker

    Bookmark   March 3, 2012 at 3:51PM
Thank you for reporting this comment. Undo
tom418

Thanks for the link, Bus_Driver, but the Home depot stores near me don't sell the item (Enfield, CT, Wallingford, CT, West Springfield, MA, and a few others). Looks like I'll have to order through Amazon.com, for a few bucks more.

I had no trouble finding the same breaker a few years ago, when I put in a well pump (240V, didn't have a choice about the trip handle then...)

    Bookmark   March 3, 2012 at 4:31PM
Thank you for reporting this comment. Undo
Ron Natalie

It used to be that the handle tie was only require if you fed the same yoke with both sides, now it's required in all cases. The GE 215 breaker isn't that hard to find...You can order it online and have it in a couple of days if you can't find it.

    Bookmark   March 3, 2012 at 6:32PM
Thank you for reporting this comment. Undo
tom_o

Approved handle ties are still allowed and are a less expensive solution. Since you're having trouble finding a common 2 pole breaker, then you'll probably not find a handle tie at the big box store. I'm guessing that part of the problem is that this breaker might be one of the 1/2 size GE breakers.

You can always call some electrical supply houses in your area, surely there is a stocking GE distributor nearby.

    Bookmark   March 4, 2012 at 11:37AM
Thank you for reporting this comment. Undo
tom418

tom_o :

Yes, it is a half size breaker. Are these becoming obsoleteted/ phased [no pun intended] out by GE?

    Bookmark   March 5, 2012 at 4:18PM
Thank you for reporting this comment. Undo
Ron Natalie

No, they're still available and in common use. Can't account for why your homecenter doesn't have them, but they are available online as I stated.

Alternatively you can move some of your single pole full size stuff from higher up in the panel down to single pole skinnies and put a full size double pole up top.

    Bookmark   March 5, 2012 at 6:12PM
Sign Up to comment
More Discussions
Replacing dimmer switch: different wire colors on new switch
My DR lights, which are controlled from two switches,...
msa6
Too much load for circuit?
I have 200 amp service to the main panel (which has...
zver11
Help with 240V 50A location
I'm trying to do a challenging kitchen layout. I will...
12crumbles
Need help Replacing old dimmer that used only 2 wires in a three way
I need advice as to which wire to connect to which...
txmat
Re-wiring range to service spa
what connectors are appropriate for joining 6-3 NMB...
justsomeotherdude
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™