old dryer 2-#6 & 1-#8 cable

Rick4343March 21, 2013

What do I need to run a outlet for a dryer with the above listed cable ? cable type? breakers? outlet type? Thank you for any help. Rick Please note I have the dryer but I have no outlet. Nothing. Starting from the breaker box is there any way to get power to this dryer ? Thanks again. Rick

This post was edited by Rick4343 on Fri, Mar 22, 13 at 11:57

Thank you for reporting this comment. Undo
brickeyee

You are not allowed to make any changes to an old 3-wire dryer circuit.

t must be replaced with anew 4-wire circuit.
Some AHJs will allow simple changes like moving or replacing the dryer receptacle, or even moving it a few inches a long as the old cable reaches the new location.

Others require the upgrade for ANY alteration

    Bookmark   March 21, 2013 at 11:40AM
Thank you for reporting this comment. Undo
weedmeister

New dryers are allowed to use the old (in place) 3-wire circuit, generally.

    Bookmark   March 21, 2013 at 2:48PM
Thank you for reporting this comment. Undo
brickeyee

"New dryers are allowed to use the old (in place) 3-wire circuit, generally."

But you are not allowed to modify the old circuit.

Limits set by local AHJ.

    Bookmark   March 22, 2013 at 11:18AM
Thank you for reporting this comment. Undo
Ron Natalie

He's not even modifying a circuit it sounds like. He wants to know if he can use some 6-2 cable he found to wire up a new dryer, and the answer is an unequivocal NO.

    Bookmark   March 22, 2013 at 1:45PM
Thank you for reporting this comment. Undo
greg_2010

I don't think it's really clear what he's asking. One of his questions is "what cable?". If he wanted to use the cable he has, why would he ask what cable?

And I don't think we'll ever hear back from him, so there's probably no point in debating what he's trying to do.

Edit: Oops, I just noticed that he changed his original post earlier today. So maybe he will stick around to answer questions and provide more info.

This post was edited by greg_2010 on Fri, Mar 22, 13 at 14:36

    Bookmark   March 22, 2013 at 2:30PM
Thank you for reporting this comment. Undo
weedmeister

yes, looking at the original, I thought the circuit was already in place and he was dealing with a new 4-wire dryer with a 3-wire circuit.

With no circuit in place, that 6/2 wire cannot be used. He needs 6/3. He'll also need a new 4-prong outlet (somebody can list the nomenclature), and a standard 2-pole breaker of the appropriate size. And the appropriate style clamp at the breaker box and perhaps the outlet box.

    Bookmark   March 22, 2013 at 2:50PM
Thank you for reporting this comment. Undo
petey_racer

No, he needs 10/3. 6/3 is WAY overkill for a dryer.

    Bookmark   March 22, 2013 at 5:41PM
Thank you for reporting this comment. Undo
elltwo

Nice catch, petey.

    Bookmark   March 23, 2013 at 6:50AM
Thank you for reporting this comment. Undo
Rick4343

I am sorry if my question was unclear. So here we go, my gas dryer died and I have been given an older, but working electric dryer. There is no plate on the back listing its specs. It has a 3 prong plug, but it does not fit a "standard" dryer outlet. The only info I can glean is the printing on the "cable" of the dryer its self. Which is [ Type SR Range Cable 2 - #6 & 1 - #8 ] So with that information my questions are. Can I still get an outlet for this type of plug, or can I change the plug? What type of cable do I need to run from the breaker box? What kind of breaker(s) do I need? Or do I need to make another trip to the scrap yard? Again sorry for any mix up and thank you for your time. Rick

    Bookmark   March 25, 2013 at 3:04PM
Thank you for reporting this comment. Undo
Rick4343

P.S. its still in the garage so at least I dont have to hall it back out of the basement. Rick

    Bookmark   March 25, 2013 at 3:09PM
Thank you for reporting this comment. Undo
weedmeister

The plate specs for mine are located inside the door. You might look there.

Otherwise, if you intend to stay within the code, the 10/3 cabling should be fine. You will probably need a 30-amp breaker. You will need a 4-prong outlet and box for the wall. You should be able to replace the cord on the dryer with a 4-prong cord.

Things get a little tricky with replacing a 3-prong cord with a 4-prong cord at the dryer. I'll let others talk about this.

    Bookmark   March 25, 2013 at 3:40PM
Thank you for reporting this comment. Undo
Ron Natalie

Most dryers made in the past twenty years have four terminals where the cord attaches with a jumper or bonding screw that bonds the case to the neutral for three wire connections.

    Bookmark   March 25, 2013 at 4:03PM
Thank you for reporting this comment. Undo
brickeyee

You can change the cord to match your receptacle, but changing the receptacle to match the cord may invoke the 'no alteration rule' in the NEC.

What size breaker is feeding the present receptacle?

That old cord sounds oversize.

Many cords use smaller conductors since they are exposed and use higher temperature insulation.

This post was edited by brickeyee on Tue, Mar 26, 13 at 12:46

    Bookmark   March 26, 2013 at 12:44PM
Thank you for reporting this comment. Undo
greg_2010

What size breaker is feeding the present receptacle?

There is no present receptacle. He's doing everything from scratch. See his update on "Mon, Mar 25, 13 at 15:04" where he explains the situation.

    Bookmark   March 26, 2013 at 1:16PM
Sign Up to comment
More Discussions
Troubleshooting Kohler 12RES Problem
I have a Kohler 12RES generator with an RDT 100 Amp...
sniffdog
Can you make a splice inside one of these?
The reason I ask is my neighbor's house was destroyed...
schreibdave
Goodbye Phone Jack: what to do with wires?
We want to remove this phone jack. It's in a useless...
maggiepatty
Same circuit for AC air handler and whole-house fan?
Hi, I've got a furnace/air handler in my attic. I was...
elofgren
Swimming pool wiring
I have 2 gfci circuits operating two pool pumps. Is...
dalemd88
Sponsored Products
Safavieh Handmade Heritage Exquisite Brown/ Ivory Wool Rug (6' Round)
Overstock.com
Modern Indoor/Outdoor Fireside Patio Mats Rugs Lonely Forest Green 6 ft. x 9
$54.99 | Home Depot
KOHLER Bathroom Memoirs Pedestal Combo Bathroom Sink in Ice Grey K-2238-1-95
Home Depot
Barrington Oil Rubbed Bronze Four-Light Vanity Fixture
$181.80 | Bellacor
Francoise Bath Bar
Lightology
Amelia Satin Nickel 3-Light Bath Bar Glass
PLFixtures
Paula Deen River House Michaels Home Bar & Hutch - River Bank - UNIR2133
Hayneedle
Secret Garden Double Gourd Table Lamp
$99.99 | Lamps Plus
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™