QO Circuit Breaker buzzing under load

bcarlson78248March 23, 2014

I have a 200 amp Square D panel with QO breakers. Due to a kitchen renovation I am using my basement workbench as a temporary kitchen area. The workbench has a 20 amp circuit with two double receptacles. The 12/2 wiring and receptacles are only about 6 months old, but I don't know the age of the breaker in the panel. The wiring only goes across the basement about 25 feet, and there is nothing else on this circuit but the two workbench receptacles.

This morning the drip coffee maker was plugged in to one receptacle ( I don't know what the coffee maker draws after it stops perking.) and I plugged a 1500 watt hot plate into the 2nd receptacle and turned it on. I was close enough to the panel to hear the breaker start humming under load, and it then stopped after about 15-20 seconds.

Does this mean I have a breaker that may fail in the near future, or does the humming just mean I'm near the max amperage on the breaker? I think this breaker is an old one they reinstalled during the heavy-up, so I don't know its age.

Thanks,

Bruce

Thank you for reporting this comment. Undo
btharmy

So, you have a 1500w hot plate and a coffee maker (likely 1500w itself) plugged into the same circuit? Do the math. 3000w/120v = 25 amps on a 20 amp breaker.

    Bookmark   March 23, 2014 at 11:17AM
Thank you for reporting this comment. Undo
ionized_gw

btharmy, the coffee maker draws much less power to keep the coffee warm after it is brewed.

Bruce, you were at max load in your testing regime when the hot plate was turned on. As the coil warms up resistance increases and current drops. I bet some of your other breakers buzz when a heavy load is on them. You are just not close enough to hear them talking to you.

    Bookmark   March 23, 2014 at 2:14PM
Thank you for reporting this comment. Undo
bcarlson78248

Thanks for the replies. It make sense that the breaker is near max amperage even if the coffee maker is just keeping coffee warm while the hot plate is running, but I've just never heard the breaker humming before.

Bruce

    Bookmark   March 23, 2014 at 9:32PM
Thank you for reporting this comment. Undo
bus_driver

Can't resist the impulse for this old joke--
"but I've just never heard the breaker humming before." It doesn't know the words!

    Bookmark   March 23, 2014 at 9:47PM
Thank you for reporting this comment. Undo
Valdemar

I vaguely remember going through a Siemens breaker catalog and seeing low-noise breakers there, which kind of implies that some amount of noise is normal in regular type breakers. I hear buzzing near my new Siemens panel, and I heard buzzing from the Zinsco panel it replaced.

This post was edited by Valdemar on Mon, Mar 24, 14 at 21:15

    Bookmark   March 24, 2014 at 9:13PM
Sign Up to comment
More Discussions
Dryer power cord next to vent
My contractor is enlarging the dryer vent hole in the...
phil2015
Confused & need help please
I know just about zero when it comes to electricity....
bicyclegirl1
Two fans on same circuit in different rooms, can't get wiring right
So here's the situation. I have two ceiling fan/lights...
jenfarino
1 of 2 security light bulbs keep going out, do i need a new light?
I have a security light fixture in my carport that...
tlbean2004
Subpanel Question
I have a 100 amp panel being fed by #4 awg copper wire I...
Calo Renovations
Sponsored Products
GE 18 in. White Direct Wire Fluorescent Undercabinet Light with Pull Chain 16685
$14.97 | Home Depot
Rochelle 32 Inch High Four-Light Outdoor Wall Light-White
$150.10 | Bellacor
GE 36 in. White Super Slim Linkable Fluorescent Undercabinet Light 10460
$29.97 | Home Depot
America Basket Company Woven Maize Full-Load Metal-Frame Lined Hamper
Overstock.com
Handmade Wooden Carved Indian Man Floor Lamp
ParrotUncle
18 Inch Chrome Shower Door Handle with Knob
TheBathOutlet
Two Dot Highballs - CLEAR/GOLD
$50.00 | Horchow
Cup of Light Pendant
| Dot & Bo
© 2015 Houzz Inc. Houzz® The new way to design your home™