electric water heater wiring

arichard21March 22, 2007

okay, we are in the process of re wiring alot of our basement to update it. i am about to run all new wire to the water heater. currently it is 10-3, but there is no nuetral. the only wires comeing from it are a red, black and a ground screw. as of now the white wire in the 10-3 is cut off.

i want to replace it with 10-2, but my buddie says i cant and HAVE to use 10-3, but when i told him the white wire is not being used he just says to clip it off. so doesnt that in effect make it the EXACT same as using 10-2?

i dont understand his logic! maybe someone here can help me!

Thank you for reporting this comment. Undo
bus_driver

10-2 with ground is suitable for 240 volt water heaters up to 5500 watts. Your "buddie" is not a good source for electrical information.

    Bookmark   March 22, 2007 at 7:02AM
Thank you for reporting this comment. Undo
arichard21

thanks bus driver, i was starting to get worried. i already purchased the 10-2 and it is roughed in to the new panel and ready to hook up!

btw, when you say up to 5500 watts, is that total or each element?

    Bookmark   March 22, 2007 at 7:08AM
Thank you for reporting this comment. Undo
normel

That would be per element since only one element operates at a time.

    Bookmark   March 22, 2007 at 8:05AM
Thank you for reporting this comment. Undo
zzeasy

Posted this in Plumbing, then saw this thread- any suggestions?

Helped a friend install a new Sears 50 gal. (#32666) yesterday and today they ran out of hot water after shave/shower. Old heater was a 40 gal. single element wired supply-black-to-heater-black and supply-white-to-heater-red. New heater is 2 element and says electric supply is wired 1 lead (used white) to yellow and 1 lead (black) to the black and the blue water heater wires. Since neither of us can get to the heater until after work today to check the obvious (1 wire not connected) I just thought I'd check in the meantime to see if this sounds correct and what else to check. Thanks!

    Bookmark   March 29, 2007 at 10:27AM
Thank you for reporting this comment. Undo
bus_driver

I suspect that the new heater is not heating with the bottom element. Another suspect is that the dip tube may be broken/missing.

    Bookmark   March 29, 2007 at 10:46AM
Sign Up to comment
More Discussions
Inspection Report
Had a gorgeous 1909 house inspected yesterday and don't...
cmae17
Subpanel Question
I have a 100 amp panel being fed by #4 awg copper wire I...
Calo Renovations
Garage florescent light flickering - bulb or fixture problem?
I replaced the GE F40 RES garage lights with a GE F40...
bibbus 7b
Humming Transformer
Last summer the POCO replaced the transformer on the...
mike_kaiser_gw
Installing 220/240V. 50/60Hz appliances from Europe
I hope to install a "Domino" modular system...
panchoandlefty
Sponsored Products
Dyson AM08 Pedestal Fan
$449.99 | FRONTGATE
Nostalgia Electrics Coca-Cola Series Pop-Up Hot Dog Toaster
Overstock.com
Switch Plate Tags Ant Brass ISLAND Switch Plate Tag 1 11/16" W
The Renovator's Supply, Inc.
Ecarpetgallery Pop Art Rock and Roll Rug - Blue - 45280
$89.99 | Hayneedle
Frontgate Misting Outdoor Fan
$149.50 | FRONTGATE
Toledo Old Silver One-Light 14-Inch Outdoor Pendant
$334.00 | Bellacor
Scotch Club 17 Pendant - Marset
$593.00 | HORNE
Virtu USA VTW-128A-BN Koz+� Collection Towel Warmer in Brushed Nickel
$329.00 | Blue Bath
© 2015 Houzz Inc. Houzz® The new way to design your home™