mysterious part inside subpanel

jimmyATcofcFebruary 20, 2014

I have a question about a subpanel that I'm getting ready to use. The attached picture that I found on the web seems to be of an identical panel. My question is: what is the gadget that has the ground wires wrapped around it in this picture? Surely that is not its intended purpose.

thanks

Thank you for reporting this comment. Undo
bus_driver

That part is from something else. The panel probably has a label inside that specifies the proper ground bar kit. Easier to read before the panel is installed.

    Bookmark   February 20, 2014 at 11:35PM
Thank you for reporting this comment. Undo
joefixit2

That is a bonding jumper. When the panel is used for service equipment (main) you swing that down and push the round end into one of the holes on the neutral bus and tighten the screw back up, bonding the cabinet to the neutral. When it is used as a sub panel you remove it and install a proper ground bus or a lug to the cabinet, isolated from the neutral bus..

This post was edited by joefixit2 on Fri, Feb 21, 14 at 0:21

    Bookmark   February 21, 2014 at 12:05AM
Thank you for reporting this comment. Undo
Ron Natalie

JoeFixit nailed it. The only thing I would add is that wrapping the ground wire around this is NOT an approved way of grounding anything. You need to get an appropriate ground terminal and install it in the panel and land the ground on that.

The proper part can be had for under $10 from any electrical supply, online, or even many of the home centers.

    Bookmark   February 21, 2014 at 9:39AM
Thank you for reporting this comment. Undo
hexus

the panel is also installed illegally, among other things.... (backfed breaker isn't secured)
If mounted horizontal like that, on must be the up position, and off down.

Article 240.81 Indicating.
Circuit breakers shall clearly indicate
whether they are in the open âÂÂoffâ or closed âÂÂonâ position.
Where circuit breaker handles are operated vertically
rather than rotationally or horizontally, the âÂÂupâ position of
the handle shall be the âÂÂonâ position.

This post was edited by hexus on Fri, Feb 21, 14 at 19:20

    Bookmark   February 21, 2014 at 7:11PM
Thank you for reporting this comment. Undo
Ron Natalie

I think that one cable coming in is a load not the feeder. The panel is a "main lugs" panel which the two hots fill the two large terminals just to the right of the 20A breaker.

    Bookmark   February 21, 2014 at 9:46PM
Thank you for reporting this comment. Undo
hexus

The lugs are empty. Unless this picture was taken before the feeder was pulled in and landed, it would have to be being energized via backfeeding the breaker.

    Bookmark   February 22, 2014 at 1:30AM
Thank you for reporting this comment. Undo
jreagan_gw

I suspect the OP found the image at some "bad electrical installations" website.

    Bookmark   February 22, 2014 at 11:00AM
Thank you for reporting this comment. Undo
Ron Natalie

Holy crap Jreagan. You're close. It's part of some potheads goofball grow light system....

You can read the rest of it's description at the link below...

Here is a link that might be useful: Potheads should stay away from electricity

    Bookmark   February 22, 2014 at 11:36AM
Sign Up to comment
More Discussions
How to get garage freezer to work in cold weather
I have a 7-year-old GE refrigerator/freezer in my unheated,...
amyf5
Please Critique Low-Volt (Home Automation) Plan/Proposal
GW/Houzz Community, As always, I want to thank this...
Andrew K.
ARGH! no boxes
Went over to my daughter's house to help them change...
Ron Natalie
Reuse electrical panel
I replaced a 24 circuit Square D panel with a new 40...
zver11
Well this sucks
Just when you thought the idiot popup ads in the gardenweb...
Ron Natalie
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™