outlet stopped working

mori1February 6, 2012

The outlet for my computer stopped working. This happened before 2 years ago and I simply replaced it. Well this time that didn't work. I finally had to breakout my receptacle analyzer/tester. The outlet is wired correctly but the second light is dimly lite. Does that mean that there something wrong with the neutral wire?

Thank you for reporting this comment. Undo
Ron Natalie

Depends which bulb is the "second" one. There's no standardization on the testers. One bright light and one dim light probably means either the neutral or the ground (we can't tell from the description) is not connected.

If all the connections are tight on the receptacle you replaced, you'll have to check earlier ones in the circuit.

    Bookmark   February 7, 2012 at 8:44AM
Thank you for reporting this comment. Undo
mori1

Trust me the connections are tight. I didn't put in back in the wall after testing it for the fifth time. The problem is all the other outlets and light switch in the room work just fine. I did do voltage check with a multimeter(?) this morning and while the other outlets read 120.7 volts. The outlet in question is 00.3.

    Bookmark   February 7, 2012 at 8:55AM
Thank you for reporting this comment. Undo
kurto

What about the connections on the "other end" of the cable that's supplying your outlet? Are the connections tight there as well? There's a broken connection somewhere. Might be time to call an electrician.

    Bookmark   February 7, 2012 at 9:26AM
Thank you for reporting this comment. Undo
mori1

I'm not sure where the line leads. Its the only outlet with one hot and neutral wire. All the other outlet in the room have two each.

    Bookmark   February 7, 2012 at 9:43AM
Thank you for reporting this comment. Undo
Ron Natalie

It sounds like an illegal installation, if you haven't a clue what you're working with, it is time to call an electrician. The presence of enough induced load to light the light dimly most likely points to a piece of wire connected tot he receptacle that is not connected on the other end to *ANYTHING*.

    Bookmark   February 7, 2012 at 10:18AM
Thank you for reporting this comment. Undo
greg_2010

I'm not sure where the line leads.

It's time to make an educated guess. Choose either the outlet to the left or right of the problem outlet and open it up and check the connections there.

    Bookmark   February 7, 2012 at 10:38AM
Thank you for reporting this comment. Undo
mori1

Thanks Greg 2010, your right. Its not like I don't have the time. Can't afford an electrician and I enjoy trying to figure things out.

    Bookmark   February 7, 2012 at 10:44AM
Thank you for reporting this comment. Undo
greg_2010

It could also be an outlet on the other side of the wall in another room. Basically, odds are that it'll be the closest outlet.

While you are opening up the outlets, I'd suggest moving any 'backstabbed' connections to the screws. The backstab feature is notorious for causing bad connections.

And wrap the wire clockwise around the screws so that it gets pulled into the screw as you tighten it.

    Bookmark   February 7, 2012 at 11:09AM
Thank you for reporting this comment. Undo
mori1

Greg2010,
Thank you so very much for your help. After two trips to Home Depot (who knew they made outlets without the green ground screw)the outlet is working. I ended up having to replace the other three outlets in the room. One of the outlets was badly corroded on the neutral side. There was one with the wires in the back like you mention so I undid that one. The last one was slightly melted on the neutral side. After I finished, the outlet that originally wasn't working, worked just fine. As it turned out there was nothing wrong with it. So thank you again.

    Bookmark   February 7, 2012 at 3:20PM
Thank you for reporting this comment. Undo
yosemitebill

mori1,

What you are describing does not sound good.

Is the wiring in the walls that you are working with copper or aluminum?

Does the wiring have a "grounding conductor" aka a "ground" running along with with the hot & neutral?

    Bookmark   February 7, 2012 at 4:40PM
Sign Up to comment
More Discussions
Outdoor subpanel as AC disconnect
Can we use an outdoor subpanel as an AC disconnect?...
ylmzm
1 of 2 security light bulbs keep going out, do i need a new light?
I have a security light fixture in my carport that...
tlbean2004
Power to shed
Looking to run one 20 amp circuit to my shed and I'm...
ohio45424
Please Critique Low-Volt (Home Automation) Plan/Proposal
GW/Houzz Community, As always, I want to thank this...
Andrew K.
Troubleshooting Kohler 12RES Problem
I have a Kohler 12RES generator with an RDT 100 Amp...
sniffdog
Sponsored Products
Georgian Design Solid Brass Double Toggle and Decora Plate
Signature Hardware
'Live Well' Vanity Plate Wall Sign
$19.99 | zulily
Vintage Giclee Glow 13 1/2" Antique Brass Swag Pendant
Lamps Plus
Polished Brass Outdoor Wall Sconce
$106.00 | Bellacor
Westinghouse Outdoor Lanterns. 2-Light Outdoor Bronze Wall Lantern with Aluminum
$72.84 | Home Depot
Secret Garden Niko Swing Arm Wall Lamp
Lamps Plus
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™