Trying To ID This Transformer

benesessoFebruary 28, 2013

Found this new xformer in a box--unknown source. Too many wires for my simple brain.

I need 24v from 120v.

Measured the resistance between the two "primary?" black/white wires, 6.3 ohms. That's like ~20amps at 120v!

Hopefully the input resistance/impedance goes way up when it's energized.

Google search of the numbers was no help. Any ideas?

Thank you for reporting this comment. Undo
benesesso

Just remembered, it came from an APS battery backup power supply for a computer. It was fed from a pair of 6v sealed batteries.

OK, 6V (I think the batteries were in parallel) up to 120v. Looks like I'm out of luck here.

    Bookmark   February 28, 2013 at 4:35PM
Thank you for reporting this comment. Undo
bus_driver

When energized by AC power, the inductive reactance serves to limit the primary current exactly as higher resistance would do.

    Bookmark   February 28, 2013 at 6:02PM
Thank you for reporting this comment. Undo
yosemitebill

If this was used for a UPS, then most likely the black & white wires are the Secondary.

The two 3-wire pairs are the Primaries - the same gauge primary/secondary was probably the AC line input (with surge suppression, RFI filtering and relay switching) in normal operation.

The heavier gauge wires were probably from the inverter output and used the transformer to produce the stepped up voltage when in UPS mode.

    Bookmark   February 28, 2013 at 9:03PM
Thank you for reporting this comment. Undo
benesesso

Thanks. Guess I'll have to pop ~$10 for a 24v eBone special.

    Bookmark   March 1, 2013 at 12:15PM
Sign Up to comment
More Discussions
Doorbell goes off by itself.
Can anyone tell me why this would happen? It's a wired...
stu2900
Reuse electrical panel
I replaced a 24 circuit Square D panel with a new 40...
zver11
Replacing dimmer switch: different wire colors on new switch
My DR lights, which are controlled from two switches,...
msa6
new wiring project
I have a water damaged room I will soon be renovating....
CharlesInVT
A/C wired to main panel only?
I had 2 electricians come out to bid upgrading my service...
frank_diy
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™