running electric to a Mobile mini unit

acokpiFebruary 11, 2013

I have a 60amp box running to an out building from the house. getting a temorary mobile mini unit that has a 100amp panel box. Can I run an appropriate gauge wire from the 60 amp to the 100 amp sub panel? I only need 40 amps in the mobile unit.

Thank you for reporting this comment. Undo
Ron Natalie

You can put subpanels that are larger in capacity than your feeder is. That's fine. You must put a breaker in the feeding panel sized to the ampacity of the feeder wires, so if 40A is what you need you can use #8 copper in the feeder and a 40A breaker. If you actually have 40A of load (as opposed to needing a 40A feeder), you may wish to size things up to #6 and a 60A feeder breaker.

I don't know what a "mobile mini unit" is, but I suspect you may need to install a grounding system for it as well.

    Bookmark   February 12, 2013 at 8:31AM