Adding circuit to existing conduit

globe199February 3, 2010

I've got a conduit used for a 50A hot tub circuit. The conduit runs along the outside of the house to a small subpanel with a GFCI, then connects to the tub.

At some point I want to rewire my garage. I'm wondering if there's room in the conduit to run a 60A circuit to the garage. I would use the existing conduit up to the hot tub subpanel, then run a new conduit out the other side of the sub to the garage.

Just guessing, but the conduit is maybe 1-inch. Anyone have an opinion on whether there's enough room? Thanks.

Thank you for reporting this comment. Undo
Ron Natalie

Well it depends on how many wires and what size and what the conduit is made out of.

There are three problems.

1. For THWN @50 amp they probably used #8 wires, you can technically fit 9 in there, but
2. For 60 amp you need #6. Further with that many current carrying conductors in the same conduit you need to derate. Either way it won't fit (and you #8 may not be sized big enough).
3. If there are 3-4 #8 wires in 1" conduit, it's going to be a bear to pull more in there anyhow.
4. (ok I lied, four things), if by "subpanel" you mean one of those spapack things (essentially a disconnect with a GFCI built into it) there's not a whole lot of room inside it for pulling through extra conductors.

On the other hand, unless you need it for protection of physical damage, you may not even need conduit. It's required for the pool/spa, but you can possibly get away with suitably sized cable.

    Bookmark   February 3, 2010 at 1:18PM
Thank you for reporting this comment. Undo
globe199

That's what I figured. Probably going to need a whole new conduit. OK, thanks.

    Bookmark   February 3, 2010 at 2:15PM
Sign Up to comment
More Discussions
Garage florescent light flickering - bulb or fixture problem?
I replaced the GE F40 RES garage lights with a GE F40...
bibbus 7b
Installing 220/240V. 50/60Hz appliances from Europe
I hope to install a "Domino" modular system...
panchoandlefty
Need to Understand GFCI Requirements.
I posted this in the remodeling section, but I think...
homechef59
Goodbye Phone Jack: what to do with wires?
We want to remove this phone jack. It's in a useless...
maggiepatty
can homeowner so electrical work in his own home ? (above ground pool)
I live in Western ma and I'm having an Adobe ground...
growingadvice
Sponsored Products
25" Granite Vanity Backsplash
Signature Hardware
Floral Blue Silhouette Bronze Balance Arm Floor Lamp
Lamps Plus
MaxLite ELLF270UN50 MaxLite StaxMAX LED Flood Lights
EnvironmentalLights.com
Firebird Pendant by Tech Lighting
$292.00 | Lumens
Safavieh Handmade Heritage Kermansha Green/ Gold Wool Runner (2'3 x 10')
Overstock.com
Modern Fan Company | Flow Ceiling Fan
$384.00 | YLighting
© 2015 Houzz Inc. Houzz® The new way to design your home™