breaker size for motorhome

instengFebruary 10, 2014

I'm looking at running a wire out from my main panel to a pole in my pasture to hook up a motorhome or travel trailer. The distance should be less than 100'. I'm trying to find out what size breaker I will need to handle the load for a typical motorhome. I don't know what the power requirements are since I don't own one it is so when friends come to visit I can have a plug for them to use. I have a lot of 8 gauge wire direct burial which I could use on a 40amp breaker. Or should I go up to a 50 amp and run a 6 gauge wire? If I use the 6 gauge I will need to buy some wire.

Thank you for reporting this comment. Undo
Ron Natalie

30 to 50 Amp "shorelines" aren't uncommon for motorhome. The bigger their land yacht, the more power they typically use.

At 100 feet I'd be inclined to size up to 6 gauge just so the voltage drop if they actually pull 30A isn't a problem.

    Bookmark   February 10, 2014 at 4:01PM
Thank you for reporting this comment. Undo
insteng

Thanks, originally I was going to install a 50 amp breaker with 6 gauge, but I got the 8 gauge free. I need to see if I can get some 6 gauge like that. It would not hurt to have it oversized for the reqiured power. The motorhome would have it's own breakers to handle it if they overloaded a circuit inside.

    Bookmark   February 10, 2014 at 5:40PM
Thank you for reporting this comment. Undo
joefixit2

RV circuits can easily get you into trouble if you are not sure what you are doing, a 50 amp hookup will take 4 wires and 240 volts but a 30 amp hookup is only a 3 wire 120 volt circuit. On all but the biggest of movie star type motorhomes all of the loads are 120 volts, and a normal RV with a 50 amp hookup utilizes the incoming 240 volts as two 120 volt lines. Seen more than one RV get fried by someone running 240 volts into a 30 amp TT hookup.

So legally you can only use a 30 amp breaker on your #8s if you are connecting directly to a 30 amp TT receptacle. About the only way you can cover all the bases is with a special RV panel which would contain a 20,30 and 50 amp receptacle with circuit breakers.

What type of wire are you using, I assume it will be underground?

This post was edited by joefixit2 on Mon, Feb 10, 14 at 20:57

    Bookmark   February 10, 2014 at 6:37PM
Thank you for reporting this comment. Undo
Ron Natalie

The common way to do it is to install a L21-50R (50A 120/240 receptacle) and make some adapters that mate to whatever RV's you are expecting.

    Bookmark   February 10, 2014 at 10:23PM
Thank you for reporting this comment. Undo
joefixit2

This is how we do it here.

This post was edited by joefixit2 on Mon, Feb 10, 14 at 22:45

    Bookmark   February 10, 2014 at 10:40PM
Thank you for reporting this comment. Undo
insteng

"What type of wire are you using, I assume it will be underground?"

I have some armored direct burial cable I got free. I will check with my friends and see which plug they need and wire it accordingly.

    Bookmark   February 11, 2014 at 10:26AM
Thank you for reporting this comment. Undo
ionized_gw

The friends may already have some adaptors that they keep in the RV, but beware, they may be ill-advised.

    Bookmark   February 11, 2014 at 2:57PM
Thank you for reporting this comment. Undo
petey_racer

If you don't know what you will be using and possibly have different things the post "Posted by joefixit2 9 on Mon, Feb 10, 14 at 22:40"
is BY FAR the best way to go.

    Bookmark   February 11, 2014 at 4:19PM
Thank you for reporting this comment. Undo
ionized_gw

That does look pretty slick. It could be very convenient if your RV camp is going to get a lot of use. How much do they cost? It must qualify as a sub panel from the look of it.

For some reason, it reminds me of a 240V (think air conditioning) disconnect that doubles as an outdoor, 120V, GFI outlet.

    Bookmark   February 11, 2014 at 4:56PM
Sign Up to comment
More Discussions
Too much load for circuit?
I have 200 amp service to the main panel (which has...
zver11
Need help Replacing old dimmer that used only 2 wires in a three way
I need advice as to which wire to connect to which...
txmat
Reuse electrical panel
I replaced a 24 circuit Square D panel with a new 40...
zver11
ceiling fan, fan works but lights do not
I have 2 kids and one threw a toy that hit one of the...
katy_bug
Insulation in electrical box
While in my attic the other day I saw an open electrical...
sgilliatt
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™