wiring a 220v oven

carny55January 2, 2007

My electrician asked me for the amperage on a new electric oven. He wanted to know what wire gauge to use. The manufacturer's info showed that the device used 3.6 KW on a 120/240v line. (And also showed 2.7 KW on a 208Y/120v line).

Well, that confused us all. As I understand Watt's law, that would imply a 15 amp circuit for 240V (3600w/240v=15a). We called the home improvement store (Lowe's) and they said 30 amp circuit. And use 10 gauge wire.

So my question is which is correct? Should it be 30 amp since the 240v is made of 2 120v wires and that amperage would be 30 amp (for 3.6 KW).

And finally why is it called 220v if it's really 240v?

And what is 208Y/120 ???

Thanks,

Electrically confused

p.s. we are using 10-3 gauge wire, and a 30 amp circuit. Are we right?

Thank you for reporting this comment. Undo
petey_racer

That confused you all? I would sincerely hope it did not confuse your electrician.

Your new oven draws 3600 watts at FULL load @ 120/240v. A watt is a watt. At that point amperage is determined by the voltage. At full load this is a nominal 15 amps. This is NOT a 15 amp circuit.

Why did you call Lowes about this? All they did was sell you the thing. They are most often clueless about these matters and often give anywhere from erroneous to downright dangerous advice.

Unless the instructions SPECIFICALLY state so, all you need is a 120/240v-20 amp circuit for this appliance. Since this unit requires 120 & 240 volts you must run a 4-wire cable in the XX/3 variety. Such as 12/3 (with ground) NM cable.
IF the unit required a 30 amp circuit then 10/3 would have been appropriate.

"And finally why is it called 220v if it's really 240v?
Who calls it 220v? Not me.
That is a generic term adopted by the masses.
Actually your oven is 120/240v, NOT simply 240v. There IS a difference.

    Bookmark   January 3, 2007 at 12:13AM
Thank you for reporting this comment. Undo
brickeyee

Many code revsions ago the nominal voltages were added to the code. The nominal residential voltages are 120 V and 240 V. Both are RMS so the peak is higher by sqrt(2) = ~1.4
208 is most often seen as part of a 3 phase system, along with some other non-residential type voltage (high leg stingers, etc.)

    Bookmark   January 3, 2007 at 9:24AM
Sign Up to comment
More Discussions
Lights Flickering...
We paid an electrician to put in a ceiling light in...
regina_phalange
Help with 240V 50A location
I'm trying to do a challenging kitchen layout. I will...
12crumbles
Insulation in electrical box
While in my attic the other day I saw an open electrical...
sgilliatt
Re-wiring range to service spa
what connectors are appropriate for joining 6-3 NMB...
justsomeotherdude
Need help Replacing old dimmer that used only 2 wires in a three way
I need advice as to which wire to connect to which...
txmat
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™