Kitchen GFCI Splits

NoctuaJanuary 30, 2014

In Canadian Kitchens Code allows for 15 amp split receptacles or 20 amp receptacles. Max two outlets per run.

All Receptiveness within 1.5 meters (59 inches) must be GFCI protected.

This means in that zone i can use one 20 amp GFCI Plug with a 20 amp breaker and 12/2 wire or i could use 2 split 15 regular plugs with a dual pole 15 amp GFCI breaker and 14/3 wire.

I am wondering if i can run split 20 amp plugs off a dual pole 20 amp GFCI Breaker with 12/3 wire and still meet code... it is above minimum isn't it?

I can get the 20 amp GFCI breakers significantly cheaper than the 15s for some reason and the extra amps would be nice.

Thank you for reporting this comment. Undo
bcarlson78248

For a non GFCI breaker you could use one 20 amp dual breaker with 12/3 for a multi-wire branch circuit and then break it out at the kitchen into two 20 amp circuits. However, I don't know if there are any unique requirements for a dual pole GFCI breaker.

I think it it would be cheaper to use a standard dual pole breaker, and then put one GFCI receptacle for each circuit and wire it so it protects all receptacles downstream. I priced 20 amp GFCI breakers last week for my Square D panel and one 20 amp GFCI breaker costs a lot more than a couple of GFCI receptacles.

Bruce

    Bookmark   January 31, 2014 at 12:31PM
Thank you for reporting this comment. Undo
Noctua

Codewise, i don't think i can do that.

Only 1 set of 2 GFCI plugs/Breaker Or 2 sets 2 split plugs/ 1 dual pole GFCI breaker.

Wondering i can can split 20 amp plugs.

    Bookmark   January 31, 2014 at 7:26PM
Sign Up to comment
More Discussions
Wireless light switch for switched outlet?
So we have no overhead lighting in any of our bedrooms,...
vikingshelmut
Same circuit for AC air handler and whole-house fan?
Hi, I've got a furnace/air handler in my attic. I was...
elofgren
Grounding Service panel 200amp
Is the new NEC saying to no longer run # 4 copper wire...
36066
1 of 2 security light bulbs keep going out, do i need a new light?
I have a security light fixture in my carport that...
tlbean2004
Dryer power cord next to vent
My contractor is enlarging the dryer vent hole in the...
phil2015
Sponsored Products
Anthracite Tall Vertical Designer Radiator Heater 70 x 14 & Valves
Hudson Reed
Pre-owned Mummy Chairs by Edra - Set of 4
$999.00 | Chairish
Cheese Mill
$16.99 | zulily
Lux Collection 10" Wide Lavender Frost Pendant
Lamps Plus
LaPalma | Apta Dining Table
YLiving.com
Sample-Pier Tribeca Marble Tile Sample
$2.99 | TileBar
Modern Craftsman Bistro Stool
Overstock.com
Casual Luxury Semi-Flushmount by Feiss
$200.00 | Lumens
© 2015 Houzz Inc. Houzz® The new way to design your home™