My home has no outside disconnect! DPDT?

tony41January 6, 2010

Here in Arkansas in the county you are not required to have an outside disconnect. Of course the building contractor didn't do anything he wasn't forced too!

Service Entrance cable is not protected from load side of meter to the panel 25' away. Panel has 200 amp main breaker.

I would like to remove the meter base and replace with a combination 200 amp meter base and 200 amp overcurrent protection/disconnect.

Problem > The service entrance cable exits the meter base makes a 90 degree turn upward to the attic inside the outside brick wall. Its not possible for the entrance cable to have enough length to make new connections. I would not mind changing out the entrance cable but I see no way running new cable back in the outside wall. Would have to be surface on brick inside conduit.

Plan B - Contact Electric Coop Request disconnection of line side conductors from meter that are feed from 3" PVC underground.

Shorten the 3" conduit to accommadate installing a 200 amp Breaker/disconnect. Then connect underground service conduit to bottom of disconnect.

I would like to install a generator hook-up to this Plan B idea. Don't know if avaiable but a 200 amp DPDT switch. Top Side fused with 200 amp fuses.

Bottom pole would not need to be fused.

Thank you for reporting this comment. Undo
Ron Natalie

Most places in the country do not require an OUTSIDE disconnect. The NEC certainly makes no such requirement. Except in a few places where the entire panel is mounted outside (temperate climates such as the Southwest), I'd even say it is uncommon. I have one in my place in NC, but only because there's a whole house transfer switch also mounted outside next to the generator.

What makes you think your main disconnect isn't protecting the run from the meter over to it?

The standard procedure when making changes to the main disconnect (or stuff on the hot side of it) is to call the power company and have them shut you off.

The generator transfer switch is infact a remotely controlled DPDT switch. Mine is rated at 400A. I've got a 80KVA generator.

    Bookmark   January 6, 2010 at 10:21PM
Thank you for reporting this comment. Undo
normel

If you add an outside disconnect, you will have to replace the line feeding the inside panel with 4 conductor cable since this inside panel now becomes a subpanel.

    Bookmark   January 7, 2010 at 7:31AM
Thank you for reporting this comment. Undo
brickeyee

The service entrance cable is protected by the main in the panel against overload.

The POCO line fuse (on the distribution side of the pole transformer) provides the short circuit protection.

It is not required since it is not really of much benefit.

    Bookmark   January 7, 2010 at 9:44AM
Thank you for reporting this comment. Undo
tony41

I took forgranted that the Main in the panel protected only the Load Side and not also Line side!
Also assumed since the nearest City required Outside Disconnect that it was a NEC requirement.
Thanks for sitting me straight!

    Bookmark   January 7, 2010 at 10:40AM
Sign Up to comment
More Discussions
electrical outlet distance to radiator
how far from a radiator should a wall electrical outlet...
amsayan
Lights Flickering...
We paid an electrician to put in a ceiling light in...
regina_phalange
Replacing dimmer switch: different wire colors on new switch
My DR lights, which are controlled from two switches,...
msa6
Replacing fan speed dial back to standard toggle?
I am removing a ceiling fan and replacing it with a...
onkyokoi
Motion sensor that doesn't click
I have a motion sensor very much like the picture attached...
drmeow3
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™