60 Amp sub panel

weaseJanuary 4, 2011

I need a 60 amp subpanel for my kitchen remodel. Anyone have a link to one with 8 slots available? I can't seem to find one.

Thank you for reporting this comment. Undo
hendricus

I picked mine up at Menard's, couldn't find any online. They have all kinds. Mine is a 12 breaker 60 amp panel.

    Bookmark   January 4, 2011 at 10:11PM
Thank you for reporting this comment. Undo
spencer_electrician

You don't have to use a 60 amp panel. Use a 100 amp panel and feed it from a 60 amp breaker. The sub panel only has to be rated at or above the breaker size feeding it.

    Bookmark   January 4, 2011 at 10:31PM
Thank you for reporting this comment. Undo
Ron Natalie

Square D makes a 60A QO panel with probably dozen or more slots in it. I've got one in my house now.

Don't forget with QO's you need to buy an additional grounding terminal bar if you'r going to use it as a subpanel.

    Bookmark   January 5, 2011 at 8:18AM
Thank you for reporting this comment. Undo
lbpod

I miss Smithy123

    Bookmark   January 5, 2011 at 8:33AM
Thank you for reporting this comment. Undo
brickeyee

You may find that a 100 or 125 amp panel with a main costs less than a smaller or main lug panel.

Manufacturing volume is a big cost driver.

    Bookmark   January 5, 2011 at 9:01AM
Thank you for reporting this comment. Undo
wease

So get a 100 amp panel and buy a 60 amp breaker for it and for the main panel? Or use the 100 amp that comes with the panel and use a 60 amp at the main?

    Bookmark   January 5, 2011 at 9:48AM
Thank you for reporting this comment. Undo
terribletom

Spencer hit the nail on the head: Use any panel rated for 60A or better...and most 8-slotters on the market these days will be rated for up to 100 or 125 amps.

In the past couple of years, I've installed 8-slot panels made my Siemans, Cutler-Hammer and Square D Homeline, so there are plenty of choices out there. The big box stores carry main lug models of this size for about $25-30.

If you do get a panel with a main breaker, there's no need to "downsize" the breaker. Since overcurrent protection will be provided by the 60-amp breaker in the main panel, the "main" in the sub-panel will effectively serve as nothing more than a local disconnect.

OTOH, if you decide to install a "main" breaker in the sub-panel rather than use a pre-installed main, keep in mind that you'll also need a hold-down kit to prevent an idiot from pulling out the backfed breaker and not realizing that it is still energized (unless the power has been turned off at the main panel, natch).

    Bookmark   January 5, 2011 at 12:58PM
Thank you for reporting this comment. Undo
wease

Gotcha...and thank you.

One more thing. I've done my load requirement worksheet and wondered if I'll have any issues having a 40 amp breaker for a double oven running in a 60 amp panel. Total load was about 11,000 VA on my calcs.

Just wonder if there was a rule regarding the highest breaker in the panel vs the panel amperage.

    Bookmark   January 5, 2011 at 1:06PM
Thank you for reporting this comment. Undo
wease

bump

    Bookmark   January 6, 2011 at 12:48PM
Thank you for reporting this comment. Undo
Ron Natalie

Well it doesn't make much sense to put a branch circuit breaker in larger than the one on the feeder, but it doesn't much matter other than that. You can put 10 50A breakers in a 60A panel if you're confident that you're not going to exceed the feeder rating.

    Bookmark   January 6, 2011 at 4:13PM
Sign Up to comment
More Discussions
Replacing dimmer switch: different wire colors on new switch
My DR lights, which are controlled from two switches,...
msa6
Too much load for circuit?
I have 200 amp service to the main panel (which has...
zver11
new wiring project
I have a water damaged room I will soon be renovating....