closet definition

leslie_gardenerJanuary 23, 2010

As part of my renovations i'm converting an

11' x 11' room into a clothes closet separate

from any bedroom.

As far as electrical inspection is concerned

can this room be owner-defined

for wiring to code purposes?

Thank you for reporting this comment. Undo
petey_racer

A closet is a closet. What do you want it "redefined" as? And what difference does it make?

    Bookmark   January 23, 2010 at 7:42PM
Thank you for reporting this comment. Undo
leslie_gardener

I don't want it redefined...
I wanted to know if I can define as
a closet or is there a code definition.

In my location the difference it makes is:
No closet shall have outlets installed
and no pendant type light fixtures, as
opposed to a regular room.
I guess your code is different or you
wouldn't have asked.

    Bookmark   January 23, 2010 at 8:56PM
Thank you for reporting this comment. Undo
petey_racer

No receptacles? Really? Dumb rule IMO, but whatever.

Sure, call it a closet. Just make sure it really is a closet.

    Bookmark   January 24, 2010 at 12:40AM
Thank you for reporting this comment. Undo
awebster

The code definition for a close closet is "a non-habitable room or space intended primarily for storage of garments or apparel". Placing recepticles is your choice but there are specific clearances that need to be met for lighting.

    Bookmark   January 24, 2010 at 2:09AM
Thank you for reporting this comment. Undo
joed

I think you would need to install shelves and rods for hanging clothes in order for it to be called a closet. The hanging fixture rule I believe also states within 2 feet of shelf.

    Bookmark   January 24, 2010 at 9:26AM
Thank you for reporting this comment. Undo
brickeyee

"I guess your code is different or you wouldn't have asked."

What code is being followed?

he NEC allows receptacles, but places strict restrictions on lights since they are a source of heat and have lit many fires in closets.

Even ballasts for florescent lights get hot.

    Bookmark   January 24, 2010 at 10:27AM
Thank you for reporting this comment. Undo
jaylane

what about a can light with a cover installed towards the front of the closet near the door? I'm getting ready to do 7 closets in my new build this weekend.

thanks

    Bookmark   February 17, 2010 at 12:47AM
Thank you for reporting this comment. Undo
brickeyee

"what about a can light with a cover installed towards the front of the closet near the door?"

This usually meets the NEC rules and more but ask the local AHJ since they have the final say.

    Bookmark   February 17, 2010 at 9:30AM
Thank you for reporting this comment. Undo
Ron Natalie

As far as the NEC is concerned, you can put a surface mounted or recessed luminaire with a completely enclosed lamp, or a surface mounted or recessed luminaire, or surface mounted fluorescent (and if you're in the 2008 NEC, LED) luminaires listed for storage areas.

Incandescent luminaires with not fully closed lamps and pendants are NOT permitted.

The clearance varies but absent some indication on the luminaire itself, it's 6-12" to the nearest "storage space" depending on where and what the luminaire is.

    Bookmark   February 17, 2010 at 10:17AM
Thank you for reporting this comment. Undo
andrelaplume2

When we moved into our home there was a can our closet ceiling. I popped down the lens and put a regular 100w bulb in there. I would shut off now and then. Finally I realized something was built into the can; a safety precaution and when I scrubbed away some sprayed in builders paint I saw a 60W max warning. Well 60W was harldly usefull in the 5 X 8 closet. I had some quotes for flourecent fixture inslalls and then notices a little glass bubble bulb fixture meant fo a can in a bathroom. It fir my ceiling can and looked a bit nicer than the falt lens that had been there. The extra space the glass bubble provided allowed me to put a 100W equivalent cfl in place. They sell 150W cfls which I think are also below 60watts but I think these bulbs are too long for the can.

    Bookmark   February 22, 2010 at 3:25PM
Thank you for reporting this comment. Undo
groundrod

This might be a little late but, are you going in or coming out?

    Bookmark   February 22, 2010 at 5:05PM
Sign Up to comment
More Discussions
Motion sensor that doesn't click
I have a motion sensor very much like the picture attached...
drmeow3
How to get garage freezer to work in cold weather
I have a 7-year-old GE refrigerator/freezer in my unheated,...
amyf5
Ceiling fan wiring
I have a new ceiling fan with a light. The fan has...
jjp2121
Crawl Space Junction Boxes: inspection and capping
Hello. I'm in the process of crawl space improvement....
SparklingWater
Doorbell goes off by itself.
Can anyone tell me why this would happen? It's a wired...
stu2900
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™