My old house has two prong outlets that I want to replace with three prong outlets and add a gound wire. Do all the new grounds have to go all the way to the panel ground connector? Can I clamp some of the new ground wires to a #6 or #8 wire in a basement junction box and run the heavier ground wire from there to the panel. Thanks ya'll

Thank you for reporting this comment. Undo
billhart

They need to have a path back to the panel (don't pretend you found "ground" on a pipe somewhere), but they don't need to be individual wires all the way back. You can join up grounds, and a #12 or #14 is ok.

These are to carry the current from one fault somewhere for the time that it takes to trip the breaker, so they don't need to be bigger than the branch circuit wires and how many you join up doesn't affect wire size needed since we assume only one will be conducting fault current at a time. Connect the ground wires to any junction boxes along the route. You don't need to add additional junction boxes just for the grounds.

The ground should follow as closely as practical the route of the hot and neutral on each circuit. If a fault current has to make a big loop (hot from the panel, fault somewhere to ground, and a different path on the other side of the house back to the panel) the breaker trip time can be extended because magnetic field effects limit the current. You want a very large fault current for a very short time to trip the breaker fast, not 40 amps for a long time heating things up before the breaker trips.

    Bookmark   January 22, 2008 at 6:11PM
Thank you for reporting this comment. Undo
cobraguy

If you currently have individual wires in conduit, you can add an individual ground by pulling it through the conduit. But I don't believe you can just add an individual ground wire without it being in conduit or romex. Feel free to correct me if I'm wrong about this.

You can also protect a circuit with a GFCI and add 3 prong plugs. There will be no equipment ground and you must label the outlets accordingly.

    Bookmark   January 23, 2008 at 7:27AM
Thank you for reporting this comment. Undo
arichard21

I am going to agree with cobra guy on this... ALL of your conductors need to be in the same casing, weather it be conduit or sheathing (romex). The best course of action like corbaguy suggested is to gfi protect.

    Bookmark   January 23, 2008 at 7:54AM
Thank you for reporting this comment. Undo
normel

OK Cobra, I will correct you. You are allowed to run a ground wire separate from the other conductors when grounding an otherwise ungrounded circuit [250.134(B)Exception 1]. However, it is usually just as easy (or difficult) to replace the entire cable with grounded cable.

    Bookmark   January 23, 2008 at 9:21AM
Thank you for reporting this comment. Undo
cobraguy

Thanks Normel. I actually came across one of Brickeyees posts on another thread that said the same thing. My thought process was running THHN through the house and not being in conduit.

    Bookmark   January 24, 2008 at 8:30AM
Sign Up to comment
More Discussions
A/C wired to main panel only?
I had 2 electricians come out to bid upgrading my service...
frank_diy
Reuse electrical panel
I replaced a 24 circuit Square D panel with a new 40...
zver11
Doorbell goes off by itself.
Can anyone tell me why this would happen? It's a wired...
stu2900
Ceiling fan wiring
I have a new ceiling fan with a light. The fan has...
jjp2121
Multiple Fluorescent Ballasts in one light fixture
Hello GardenWeb. I'm not new here, but couldn't log...
MikeM21
© 2015 Houzz Inc. Houzz® The new way to design your home™