Oven design options with current wiring...

mlo1January 2, 2012

Hello...We have a desire for a seperate 27" wall oven and 30" induction cooktop vs our current slide in Range. The home was built in 2008 and to my surprise has a 75' long aluminum range feed on a 40amp breaker. The sheathing reads Stabiloy AA-8030 AL type SE style R XHHW-2 600v CDRS 6 awg and is a 3 wire. The panel is a Siemens 30 slot 200 amp.

Is this current wiring capeable of what we are contemplating? It would be a very difficult circuit to re-run because of a lack of access both above and below meaning interior demo. Was hoping to sort-of look at this from a reverse engineering perspective and plan around the cutrrent circuit. We do have an un-used dedicated 20 amp 110v circuit several feet away that was originally intended for a microwave. Not sure if that helps anything. Thanks for any input!

Thank you for reporting this comment. Undo
Ron Natalie

You'll need to look at the ratings of the appliances involved. However, induction cooktops usually have a pretty healthy draw and may need to be on that range circuit by itself. There are some wall overs that could run on the 20Amp circuit if you reconnect it as a 240V (would not involve pulling new wire) circuit.

    Bookmark   January 2, 2012 at 6:49PM
Thank you for reporting this comment. Undo
mlo1

Looks like the oven is rated 240v 3.6kw 15 amps and the cooktop rated at 240v 7200w 30 amps.

The 30 slot panel is full with many of the breakers already what I will call double mini's. I likely should entertain seeing about a larger panel for the possibility of having some circuits added. Seems I have read that some manufacturers panels will accomadate more breakers without upping the service rating.

Thank you for your time!

    Bookmark   January 2, 2012 at 7:36PM
Thank you for reporting this comment. Undo
dodge59

We "bit the bullet", our old range had alum wire running to it. We replaced it with copper and used that to run the induction cooktop, but at the same time ran copper for a regular 30" oven and another line for our Elux Speed oven.
Wasn't that expensive once we figured out the least invasive and easiest run for the new wiring.

I sleep a lot better at night , knowing that aluminum wire is GONE from our kitchen, alto we bought this house new in 1975 and never had a problem, but I just don't like the idea of pullin all that power across aluminum wires.

The 120 volt circuit won't help you with the oven or the induction.

Good luck on your project---try to find a "Hungry but reliable electrician"!

Gary

    Bookmark   January 3, 2012 at 7:55PM
Thank you for reporting this comment. Undo
mlo1

My electrician was the high bid and I still hired him based on a good local reputation. My up-front position was that I wanted premium quality and US made products where possible. I have been surprised more than I like with things like "backstab's" (which he ranted against in the beggining), severely twisted wires pointed out by the inspector, the aluminum range wire which he insisted I was being rediculous over, confused "ghost" circuits after sheetrock, and a panel that is maxed-out. He is now gone from the area. I wish I new a hungry pride-full sparky.

    Bookmark   January 3, 2012 at 11:42PM
Sign Up to comment
More Discussions
Replacing fan speed dial back to standard toggle?
I am removing a ceiling fan and replacing it with a...
onkyokoi
Help with 240V 50A location
I'm trying to do a challenging kitchen layout. I will...
12crumbles
Spa Capacitor question
My spa is wired for 220v. The pump motor is rated for...
pugmark
Multiple Fluorescent Ballasts in one light fixture
Hello GardenWeb. I'm not new here, but couldn't log...
MikeM21
Crawl Space Junction Boxes: inspection and capping
Hello. I'm in the process of crawl space improvement....
SparklingWater
© 2015 Houzz Inc. Houzz® The new way to design your home™