orgnovaJanuary 4, 2011

I have a gfi that has never worked. When replacing the bad? one I found out the load side was hot too. Since both sides are hot, could I just wire them together with a pigtail and connect the gfi plug?

Thank you for reporting this comment. Undo
orgnova

Just a follow up, when I turn the breaker off for that gfi, both sides are dead. I'm assuming that since they are on the same circuit, it would be ok to connect the two and connect with a pigtail to the new gfi plug.

    Bookmark   January 4, 2011 at 3:45PM
Thank you for reporting this comment. Undo
stinkytiger

Hi Mr / Ms Orgnova,

One thing to check before you wire the two hot's together is to make sure that they are on the same phase. Is the breaker a single or double breaker? If it is a double breaker there is a chance that the two "HOT" wire are on a different phase. If that is the case then you cannot wire them together.

I am guessing that the GFCI will only be protecting that one plug position. So I would take one of the hots and put a wire nut on it and tape it up. I.E. just put it out of the way. You will not have a "LOAD" side connected up to the GFCI. I would then connect up the remaining Ground, Hot and Neutral wire to your GFCI.

Not the GFCI will then only protect that one outlet because you have no downstream LOAD outlets.

Warmest regards, Mike.

    Bookmark   January 4, 2011 at 5:47PM
Thank you for reporting this comment. Undo
w0lley32

Hi! When you say that both line and load are hot, do you mean they're hot even with the GFI out of the circuit and not connected together?

If not, are you sure the line and load connexions were not reversed on the GFI? Some newer GFI's are designed not to work if it's the case.

    Bookmark   January 5, 2011 at 12:15AM
Thank you for reporting this comment. Undo
brickeyee

"Some newer GFI's are designed not to work if it's the case."

ALL new GFCIs now detect if the power is applied to the LOAD terminals in error (instead of the LINE terminals).

What are you using to check the voltages?

    Bookmark   January 5, 2011 at 3:33PM
Thank you for reporting this comment. Undo
wease

If that GFI was wired that way, shouldn't you be worried about some other possible safety issues with the wiring in the entire house? I'd have it checked out.

    Bookmark   January 5, 2011 at 5:01PM
Thank you for reporting this comment. Undo
texasredhead

Where is this GFI installed, what is its purpose, and who installed it?

    Bookmark   January 6, 2011 at 9:58AM
Sign Up to comment
More Discussions
Two fans on same circuit in different rooms, can't get wiring right
So here's the situation. I have two ceiling fan/lights...
jenfarino
Installing 220/240V. 50/60Hz appliances from Europe
I hope to install a "Domino" modular system...
panchoandlefty
Need to Understand GFCI Requirements.
I posted this in the remodeling section, but I think...
homechef59
Same circuit for AC air handler and whole-house fan?
Hi, I've got a furnace/air handler in my attic. I was...
elofgren
Wireless light switch for switched outlet?
So we have no overhead lighting in any of our bedrooms,...
vikingshelmut
Sponsored Products
5-blade Ceiling Fan in Adobe Cream Finish
Overstock.com
Pagoda 2-Light Solar 6000K 3.2 Watt LED Black Lamp Post
Lamps Plus
Lauren Outdoor Table Lamp
$229.00 | FRONTGATE
Graph Lounge Chair
| Dot & Bo
Hudson Reed Radiant Curved Plug In Heated Towel Rail 32 x 24
Hudson Reed
Green 5050 Single Row CC LED Strip Light 60/m 12mm wide Foot
EnvironmentalLights.com
Halo Table Lamp in Clear
$149.00 | LexMod
Bocci | 28.1 Single Pendant
$495.00 | YLighting
© 2015 Houzz Inc. Houzz® The new way to design your home™