electrical range installation

capt_philJanuary 14, 2010

Ok... Boat CFR's and NEC guidelines are not the same as housing.

Installing an older model stove - 3-wire vintage (it was free). Have run 6/3 to a 50A Breaker.

1) Would like the proper way to connect the neutral white wire and ground in the outlet and then in the sub-panel (can neut wht and grnd go together if I keep white and ground together in the breaker box?

thanks.

Thank you for reporting this comment. Undo
hendricus

1) Don't. Wire up the outlet for four wires hot,hot,neutral,ground and change the pigtail on the stove to a four prong to match the outlet.

As long as you have the correct wiring you might as well do this correctly all the way.

    Bookmark   January 14, 2010 at 3:25PM
Thank you for reporting this comment. Undo
capt_phil

I was not sure I could change the stove 3-wire config to a 4-wire. Than makes outlet and breaker box easy, however, I am not sure what to do with the white neutral and ground on the stove.

    Bookmark   January 15, 2010 at 8:02AM
Thank you for reporting this comment. Undo
hendricus

I don't know all the stoves but basically there will be a terminal block for 2 hots and the neutral. There should be a jumper from the chassis to the neutral connection, remove this and fasten the ground to the chassis.

    Bookmark   January 15, 2010 at 8:09AM
Sign Up to comment
More Discussions
ceiling fan, fan works but lights do not
I have 2 kids and one threw a toy that hit one of the...
katy_bug
Insulation in electrical box
While in my attic the other day I saw an open electrical...
sgilliatt
Need help Replacing old dimmer that used only 2 wires in a three way
I need advice as to which wire to connect to which...
txmat
new wiring project
I have a water damaged room I will soon be renovating....
CharlesInVT
Crawl Space Junction Boxes: inspection and capping
Hello. I'm in the process of crawl space improvement....
SparklingWater
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™