In a garage, if the outlets are wired with 12 gauge wire and protected by a 20 amp breaker....do the receptacles on the circuit need to be 20 amp OR can they be 15 amp?
Thanks

Thank you for reporting this comment. Undo
greg_2010

If there is more than one outlet (and even a regular duplex counts as two) then 15 amp receptacles are fine.

    Bookmark   January 2, 2013 at 2:13PM
Thank you for reporting this comment. Undo
brickeyee

15 amp receptacles are allowed on 20 amp circuits as long as there is more than one receptacle.

A single duplex receptacle is allowed.

The feed throuhg on the side of the 15 A receptacle is sized for 20 amps.

    Bookmark   January 2, 2013 at 2:13PM
Thank you for reporting this comment. Undo
btharmy

They can be 15a as long as there is more than one receptacle. A single receptacle will not fly but one or more duplex receptacles is fine. 2008 NEC 210.21(B)(1)

This post was edited by btharmy on Wed, Jan 2, 13 at 14:19

    Bookmark   January 2, 2013 at 2:14PM
Thank you for reporting this comment. Undo
btharmy

Don't forget, they need to be GFCI protected.

    Bookmark   January 2, 2013 at 2:20PM
Thank you for reporting this comment. Undo
Ron Natalie

If the garage is at or below grade level...

    Bookmark   January 2, 2013 at 2:49PM
Thank you for reporting this comment. Undo
btharmy

ronnatalie said "If the garage is at or below grade level..."

Receptacles in garages are required to have GFCI protection. 210.8(A)(2)

The requirement is for Garages, and also accessory buildings that are below grade (in addition to garages). Not garages and accessory buildings that are below grade. The key is the comma and the word "also". It changes the context of the sentence. Anything after the comma is in addition to the rule for garages, which is to have GFCI protection for all 120v receptacles.

    Bookmark   January 2, 2013 at 5:34PM
Thank you for reporting this comment. Undo
bus_driver

And to be sure that it is not considered a Hazardous Class, keep all premises wiring electrical devices at least 18" above the floor.

    Bookmark   January 2, 2013 at 6:18PM
Thank you for reporting this comment. Undo
Ron Natalie

btharmy is correct, I somehow had that misinterpretted in my memory. It should also be remembered that in the 2008 requirements the "not readily accessible" and garage door opener exceptions were removed.

    Bookmark   January 3, 2013 at 10:54AM
Sign Up to comment
More Discussions
Re-wiring range to service spa
what connectors are appropriate for joining 6-3 NMB...
justsomeotherdude
Multiple Fluorescent Ballasts in one light fixture
Hello GardenWeb. I'm not new here, but couldn't log...
MikeM21
Crawl Space Junction Boxes: inspection and capping
Hello. I'm in the process of crawl space improvement....
SparklingWater
ceiling fan, fan works but lights do not
I have 2 kids and one threw a toy that hit one of the...
katy_bug
Insulation in electrical box
While in my attic the other day I saw an open electrical...
sgilliatt
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™