Junction box hidden

albertmJanuary 26, 2009

My basement has two circuits running in one conduit to a junction box in the open ceiling. At the Jbox they branch into two conduits running to different parts of my basement. The Jbox appears to simply be a means of branching from one conduit to two. The wires are continuous (not cut or spliced in the junction box).

The Jbox has a solid cover. So the circuits are a continous run from the circuit panel to the outlet boxes with not cuts or splices.

Is it acceptable to enclose this Jbox in a drywall ceiling, since the wires are continuous?

Thank you for reporting this comment. Undo
jmvd20

The box must remain accessible.

    Bookmark   January 26, 2009 at 12:44PM
Thank you for reporting this comment. Undo
electricman

J boxes (junction boxes) are designed to have joints/splices in them. If EMT conduit was ran (metal pipe) the only reason that J box is there is because the electrician had more bends in his conduit than he wanted so he had to place a Jbox there due to codes. NEC code book only allows 360 degrees in a run of conduit from the panel to a junction box. He was maxed out on bends in the conduit so he placed the Jbox there to give him more pipe to work with and another 360 degrees to bend. Thats why the wires are just passing through and there is no joints in the box. If you are worried about a inspector have it inspected before you cover it. If its already passed inspection you are good to go! Tho If the wire ever needs to be replaced or a new circuit is wanted to be added. It will be close to impossible to get a fish tape through all those bends in the conduit. Though conduit is not a requirement for a residential home and romex can easily be used instead. In fact im not sure why that guy even ran conduit. I would ask a inspector or call your local electrician to double check that because the codes are different pending on where you live. I hope this helps.

    Bookmark   January 26, 2009 at 4:52PM
Thank you for reporting this comment. Undo
Ron Natalie

The conduit may be required in his jurisdiction. People don't tend to go to that length when not necessary.

I doubt it's the bend limit, the OP says it's a Y connection. Some of the conductors go one way, some go another.

    Bookmark   January 26, 2009 at 7:27PM
Thank you for reporting this comment. Undo
electricman

Yea your right I miss read that. "At the Jbox they branch into two conduits running to different parts of my basement" I was thinking 2 conduits hit a JBOX then turned out with no spices in them. That makes more sense. I still dont see a reason you could not drywall over them tho??

    Bookmark   January 26, 2009 at 7:53PM
Thank you for reporting this comment. Undo
jmvd20

Junction boxes, pull boxes, whatever term we want to use for this particular situation is beside the point. Also it makes no difference if there are splices contained inside of the box or not.

The reason that you cannott drywall over the box is because it must remain accessible - period.

    Bookmark   January 26, 2009 at 10:07PM
Thank you for reporting this comment. Undo
BStras21_gmail_com

Nice reason, hope you didn't hurt your brain on that!

    Bookmark   February 5, 2011 at 6:52PM
Thank you for reporting this comment. Undo
brickeyee

A box can be used to satisfy the 350 Ldegree bend rule without actually making a splice.

You pull the wires to the box, then continue them on unbroken.

It does NOT mean they were a continuous pule.

    Bookmark   February 5, 2011 at 11:26PM
Thank you for reporting this comment. Undo
brickeyee

360 degree (four 90s)

    Bookmark   February 6, 2011 at 8:05AM
Thank you for reporting this comment. Undo
DavidR

The code says that junction boxes have to be accessable. I don't have the reference here, but I don't recall any exceptions for junction boxes that don't contain splices. I suppose you could propose such an exception for the next code cycle.

    Bookmark   February 6, 2011 at 3:22PM
Thank you for reporting this comment. Undo
fixizin

Can a T-body be used in that situation, and if so, could it then be concealed?

    Bookmark   February 6, 2011 at 10:22PM
Thank you for reporting this comment. Undo
fixizin

... you never know... until you pore over 3,247 pages of the NEC... 2011 Edition, lol.

    Bookmark   February 6, 2011 at 10:26PM
Sign Up to comment
More Discussions
Spa Capacitor question
My spa is wired for 220v. The pump motor is rated for...
pugmark
Insulation in electrical box
While in my attic the other day I saw an open electrical...
sgilliatt
Please Critique Low-Volt (Home Automation) Plan/Proposal
GW/Houzz Community, As always, I want to thank this...
Andrew K.
Crawl Space Junction Boxes: inspection and capping
Hello. I'm in the process of crawl space improvement....
SparklingWater
Replacing dimmer switch: different wire colors on new switch
My DR lights, which are controlled from two switches,...
msa6
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™