Wire 3-Way/4-Way Switchs with 14/2

hookoodookuJanuary 23, 2010

Is it against code to use a pair of 14/2 to wire 3-way/4-way switches?

Two ways to do this:

1. Simple run a pair of 14/2 together. Use the two blacks as the red/black of the 14/3, tie the two whites together for the white.

2. Run a loop of 14/2. One set of 14/2 connects all the 3-way/4-way switches together. The other 14/2 runs from the 3-way that recieves the power (connect ONLY the neutral) out to all the lights on the circuit and terminating at the other 3-way (where you connect ONLY the hot to the end of the 3-way).

Thank you for reporting this comment. Undo
petey_racer

This is a violation of NEC 300.3(B).
The conductors of a circuit must be in the same raceway, conduit or cable.

If you need the text we can post it.

    Bookmark   January 23, 2010 at 3:22PM
Thank you for reporting this comment. Undo
groundrod

petey
wouldn't 300.3(B)(3) allow nonferrous wiring methods like NM when used with plastic boxes? while I prefer the use of three conductor cable, if run in close proximity to each other, I believe the use of two nm cables is code compliant.

    Bookmark   January 23, 2010 at 3:45PM
Thank you for reporting this comment. Undo
petey_racer

Persoanlly I don't think it applies. They specifically state that: "the conductors shall comply with the provisions of 300.20(B)"

300.20(B) specifically references "individual conductors".

    Bookmark   January 23, 2010 at 5:33PM
Thank you for reporting this comment. Undo
groundrod

I don't believe 300.3(B)(3) would include the words cable and cords if it only applied to individual conductors. NM and plastic boxes would comply with 300.20(B) because it says where, and since we don't have any "where" single conductors pass through ferrous metals, we are by default already in compliance.

    Bookmark   January 23, 2010 at 6:18PM
Thank you for reporting this comment. Undo
joed

If it is permitted it is definitely not permitted to double up or parallel the wires. Use them only as single wires.

    Bookmark   January 24, 2010 at 9:29AM
Sign Up to comment
More Discussions
ARGH! no boxes
Went over to my daughter's house to help them change...
Ron Natalie
Motion sensor that doesn't click
I have a motion sensor very much like the picture attached...
drmeow3
new wiring project
I have a water damaged room I will soon be renovating....
CharlesInVT
Please Critique Low-Volt (Home Automation) Plan/Proposal
GW/Houzz Community, As always, I want to thank this...
Andrew K.
Well this sucks
Just when you thought the idiot popup ads in the gardenweb...
Ron Natalie
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™