Generator Transfer Switch Question

tavertyJanuary 30, 2012

I recently installed a portable backup generator with a Reliance ProTran Q 510 transfer switch. Everything works great, except I had a question about how I installed it. My home has a 400 amp service with two 200 amp main panels in the house. There were some circuits in the first panel and some circuits in the second panel. The transfer switch comes with a black and red for each circuit and only one white and one green for all the circuits. I installed the green and white to their respective bus bars in the first 200 amp panel. Then I ran a conduit between the two panels and ran the red and black cables from the transfer switch to the second 200 amp panel. I did not bring over the white and green wire from the first panel to the second. The second panel was already tied to the first panel with a big copper ground wire.

So my question is: Is this legal and safe? I thought it was because the neutral and ground are bonded at the panel. And I thought the neutral/ground in one panel is the same as the neutral/ground in the other panel. All my circuits, whether on generator or main line check out with a line tester. I just want to make sure I'm not overloading the neutral and I'm not creating an unsafe situation.

Thank you for any feedback.

Thanks,

Scott

Thank you for reporting this comment. Undo
adinota3

No you need to bring both lines back to the secound panel and you need to keep them seperate on two different busses. The neutral (white) and the Ground wire (green) can be on the same bus in the main panel but on any sub-panel (also known as your secound panel), they must be kept seperate and the neutral bar must not be in direct contact with the panel. It usually has what looks like plastic brackets that mount to the back of the panel box keeping both the panel and the neutral bar seperate.

So it doesnt mater what kind of panel your talking about, whether you have a sub panel or main panel they must have both wires. The difference is if what you are talking about is a sub-panel you must bring both green and white lines back to the sub panel and install them on two seperate buses. *for your knowledge the main panel is the panel directly fed by your meter. Sub-panels are panels fed from another panel by a breaker or fed from a fused Main disconnect. Also if your secound panel is not fed from a breaker at the main panel and its fed directly off of the main bus from the first then it is considered a secound section of the same panel. or in your case the secound section of the main panel. But in order to be taped off from the bus on the first panel legally, both panels must be within sight of each other or else this against code.

If you need more info read more about grounding and bonding in any electrical book you can get from a barnes and noble. you might as well if your going to do that kind of work yourself. But just in case you should probably have a licenced electrician inspect the work. it should not cost much one hour at a service charge rate. Between $125.00-$150.00 (this is a NYC. rate your area might be less) not a bad idea concidering that you will at least have piece of mind its safe.

I hope this helps

-Anthony

    Bookmark   February 6, 2012 at 6:44PM
Thank you for reporting this comment. Undo
taverty

Anthony,
Thanks for the information. The second panel in my case is just another main panel. Both panels are fed by the meter not one fed by the other. They sit within 3 inches of each other and both have the thick aluminum wiring coming from the meter into the top. My meter is a 320/400 amp meter. My two main panels are 200 amp each. The neutral/ground is bonded in both main panels with a ground wire going between the two panels.

I think you're right that I should just get an electrician in to take a look. Once I have him out I'll post what he says.

Thanks,
Scott

    Bookmark   February 7, 2012 at 11:49AM
Sign Up to comment
More Discussions
Inspection Report
Had a gorgeous 1909 house inspected yesterday and don't...
cmae17
Swimming pool wiring
I have 2 gfci circuits operating two pool pumps. Is...
dalemd88
Troubleshooting Kohler 12RES Problem
I have a Kohler 12RES generator with an RDT 100 Amp...
sniffdog
Confused & need help please
I know just about zero when it comes to electricity....
bicyclegirl1
1 of 2 security light bulbs keep going out, do i need a new light?
I have a security light fixture in my carport that...
tlbean2004
Sponsored Products
Stilo Satin Nickel One-Light Incandescent 120v Mini Pendant with Flat Canopy and
$171.00 | Bellacor
Hunter Ceiling Fans Pro's Best Five Minute 52 in. Brushed Nickel Ceiling Fan
Home Depot
Standard Quilted Piazza Sham - CHARCOAL (STANDARD)
$145.00 | Horchow
Hamilton 8 Drawer 1-Door Chest - Warm Brown Cherry - HM100CH
$548.00 | Hayneedle
Quoizel Butterfly Tiffany Style Accent Lamp
$59.99 | Lamps Plus
Kani Chrome Three-Light Bath Fixture with Honey Glass
$459.00 | Bellacor
Indoor Ceiling Fans and Light: Hampton Bay Farmington 52 in. Indoor Tarnished Br
$47.97 | Home Depot
EON Resin Outdoor Conversation Set - GLC015
Hayneedle
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™