Three Way Switch setup

tom418January 2, 2012

I'm installing a switched outlet, controlled by two three way switches.

My setup is to be:

Coming into switch box number one: Power feed.

Then 14-3 Romex between Switch box #1 and Switch Box #2,

which contains switch #2 only (no other cables enter/leave).

A 14-2 will leave box #1 to run to switched outlet.

So, I want to connect Black from feed in Box #1 to black conductor of 14-3 running between the two boxes. Red and white will be travellers. In box #1, Red and white from 14-3 get connected to the two (non common, if you will) terminals of switch #1, and the common terminal of switch #1 gets connected to the 14-2 running to the switched outlet.

In all my other 3 way switch wiring, the route has been power to switch #1, then Red/black travellers "hot", with neutral carried by white, and then in switch box #2, a 14-2 running to load with the black attached to common of switch number 2. What is different here is that I'm not running a neutral between the two switches. Is this allowed? I'm running it this way, as there is less cable used.

Thank you for reporting this comment. Undo
hendricus

Ain't gonna work.

Power feed into switch #1 connect to common on 3-way switch.

3 wire cable to second switch. At switch one connect red and black to travelers and then connect same to travelers at switch #2. Connect white to common of switch #2 and remark it with black tape.

in Switch box #1 connect white from Switch #2 to black fixture wire, again remark the white wire with black tape.

In switch box #1 connect white from fixture to white from power source.

    Bookmark   January 2, 2012 at 1:44PM
Thank you for reporting this comment. Undo
tom418

So hendricus, I can conclude that red and white can't be used as travellers, only black and red, and hot from feed has to connect to common on switch one, instead of a conductor that would connect it to common terminal on switch # 2 instead. Correct?

    Bookmark   January 2, 2012 at 2:38PM
Thank you for reporting this comment. Undo
linesman

Hello tom418

Here is a drawing I made of what I think you are trying to do.
You can just re mark the White traveler wire ends with a Black marker.
Make sure you are using 2 regular 3 way switches. -- No dimmer switches !!

Hope this helps

Let us know how you made out with your wiring project

Have A Nice Day


Linesman

    Bookmark   January 2, 2012 at 6:33PM
Thank you for reporting this comment. Undo
linesman

Hello tom418

Opps

This is the way I now understand your description.. But either drawing will work. Make sure you re mark the White traverler wire ends with a Black marker.

Hope this helps

Let us know how you made out with your wiring project

Have A Nice Day


Linesman

    Bookmark   January 2, 2012 at 7:30PM
Thank you for reporting this comment. Undo
tom418

Linesman, that is EXACTLY (your Pic 2) what I'm doing. Thanks!

What caught me off guard, is that all of the (four) previous times that I've installed 3 ways switches, they were in order of FEED -> Switch 1 > Switch 2 -> Load. And when I wired these setups, the neutral was carried in the 14-3 romex, with the travellers being Red & Black.

So, once again: Thanks.

    Bookmark   January 3, 2012 at 3:24PM
Thank you for reporting this comment. Undo
hendricus

I got it after reading it again. You are using box 2 for the first switch and box 1 for the second switch.
Either way works.

    Bookmark   January 3, 2012 at 8:29PM
Sign Up to comment
More Discussions
Grounding Service panel 200amp
Is the new NEC saying to no longer run # 4 copper wire...
36066
Badly done multi-wire circuits (previous owner strikes again..)
I bought a 1940-ish house last year, for which the...
quahog
Wiring in a 1 1/2" thick wall cavity
I need to run 12/2 wire thru an existing thin wall....
baker1mich
Outdoor subpanel as AC disconnect
Can we use an outdoor subpanel as an AC disconnect?...
ylmzm
Installing 220/240V. 50/60Hz appliances from Europe
I hope to install a "Domino" modular system...
panchoandlefty
Sponsored Products
Hammered Solid Brass Double Switch Plate
Signature Hardware
Bare Bulb Ring Sconce - White Wall Plate - Brendan Ravenhill
$270.00 | HORNE
Artemide | Tolomeo Table Lamp with Shade
YLiving.com
Montana Woodworks Homestead Armoire Lacquered
Beyond Stores
Modern Thermostatic Chrome Tub and Shower Faucet Set
TheBathOutlet
Rowenta Commercial Pro Master Iron
$99.50 | FRONTGATE
Adorne 1-Port Keystone Frames
LBC Lighting
Edward Side Table
$209.99 | Dot & Bo
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™